Project: Affordable Green Upgrade to Net Zero Energy
Last Post 01 Jun 2010 03:29 PM by adkjacUpstateNY. 0 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
adkjacUpstateNYUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:167

--
01 Jun 2010 03:29 PM

1988 1.5 story home w/ heat pump/electric backup

Project: Affordable Green Upgrade to Net Zero Energy

Specs today:
2000sqft standard 2x6 fiberglass batt, OSB sheathing not taped, no building wrap, no rim joist insulation, and vented roof leaking warm inside air. 40millionBTU annual heat load.

R-5 true whole wall R (R-19 glass batts perform poorly in leaky wall at low outside temps)

R-15 attic/roof (R-38 glass batts with venting leaking heated air out)

R-1 cellar (R-11 batts 1" off wall, short of floor by 1')

R-.5 rim joist (no insulation, no caulking)

R-1 windows (double pain not well installed, no spray foam used)

Passive solar ( Great southern exposure, poorly adapted, few windows to south, 2 garage doors dominate)

Plan; divide 40 million BTU 1/2 shell retrofit, 1/4 low temp heat, source 1/4 warmer temp HVAC system
1-Insulation retrofit:

R of the existing shell may be as low as R-7.Retrofit to true R-20 whole assembly at 25 pascals say. (makes ICF sound good doesn't it!?) Plan; add used 3" ISO roof deck board over existing OSB sheathing, tape both well, foam joints. Entails removing siding, adding firring & residing. Roof; needs replacement so add 3" ISO to roof, tape seams, fir, vent, reroof with 50 year shingles.

Windows; remount, foam seal, retrim, add pane to North windows, add windows to south for added passive gain. Cellar; remove insulation, spray CC Soy foam 2" including rim joist, replace fiberglass and build wall to floor, add no paper waterproof ext drywall. 40mBTU/2=20mBTU

2-Divide heat load: 1/2 extreme cold, 1/2 other temps

Coldest temp heat source- sealed combustion wood heat use during all hours of lowest temperatures (say 30 degrees F and lower) Burn 10 million BTUs of wood. Carbon neutral renewable plenty in this area in waste wood alone. Cost $200/yr. 16mBTU/ton(70%)=11

Primary base load heat source- Altherma Daiken air to water unit. Use mainly at 32 degrees and higher, if temp set back to 45 degrees/vacation lower delta T, let it run. COP if used in this manner could go up at least 1 maybe 2 points. Say seasonal COP hits 3.5, 9 million BTU needed+. 3400BTU/KWHx3.5COP~12,000BTU 9mBTU/12,000BTU=750KWH needed. = 1KW PV array. With summer AC double both. 1500KWH=2KW PV array.

Project Costs: (Material only, Subcontractors would charge at least 2M to make a reasonable fee, more if general contractor with subs.)

$15,000 Shell insulation other.

5,000 Wood heat Pellet stove/sealed woodstove/fireplace w/ chimney.

10,000 Daiken Altherma electric heat pump, with solar package for hot water. Domestic water costs drop to ~1/6. (6000KWH annual/4=1000KW domestic water)

10,000 Photo Voltaic PV Array Spring of 2011 price is predicted to be wholesale $1/watt. 28 panels and 2 inverters 5.6KW system. 5,000KW annual production. 5000KW minus 1000KW (hotwater) minus 1500KW (HVAC) = 2500KW other use. Home reduced to 2500KW by monitoring use/making changes. Go for 100watts continuous use with 6 hours of added 400watts use. Need super efficient small refrigerator kept in cool part of home, next to outside wall winters with cold wall mod. Wash with cold water, new low water unit, dry on line.

2000 Monitoring/Control System to keep tabs on all, log all and control all and make improvements.

$50,000 Total Project Cost $25/sqft materials for this 2000sqft retrofit $50-75/sqft contracted. And double these numbers again if all is modernized to todays idea of larger bedrooms, solid surface coutertops, all hardwood floors, tile baths with frameless glass enclosures.

Net Zero Energy Home if project completed possibly and very green if soy and recycled foam are part of the renovation.

Version 1.0 June 1, 2010

Please discuss this and your projects, insights corrections welcomed.

aj

 

 

 

 

 