Geothermal and Air Heat pump Temps for AIR COMFORT
Last Post 30 May 2012 12:25 PM by joe.ami. 124 Replies.
Author Messages
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
02 May 2012 10:23 AM
In a usual range of at a needing to heat inside on a 47 to a +5F  outdoors -
Would it be possible to get to a graphical curve or a clear reference of a description at different dropping temperatures of :
What are some heating outputs comparing a highest speed blower stage of usual higher efficiency GEO to highest efficieny AIR heat pumps by a same air temperature at a same air volume and a same air speed then?

what is happening with Geo on a same curve vs air heat pumps as standing alone in an application with out an enrgy loss by a duct loss ? I have an opinion. Commercially- Carrier and other old consoles are still in offices and restauarants in very old resorts; and in warehouses, and in school gymnasiums. Geo Residential consoles are in more literature than those motel heat pumps  and all is in regards to a previous Dana1 and joe.A  discussion:
minisplit web site DOE
www.      nrel.gov/docs/fy11osti/52175.pdf  ( i recommend just copy and paste )

?
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
02 May 2012 04:34 PM
I've only seen a handful of geo-air systems up close & personal, and didn't instrument them, but they were all pretty cool in the draft, but the houses were quite comfortable. Most are not modulating systems the way mini-splits are, but many are multi-stage. (This is true of most ducted air-source systems I've seen too.)

It's not hard to design the duct systems to minimize wind-chill from tepid air systems in McMansions, a bit tougher in a 1000' Cape style house.
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
03 May 2012 08:29 PM
Dana is correct. Duct systems are often under valued by buyers and code minimum installers yet the root of much dissatisfaction.-
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
03 May 2012 11:14 PM
Most systems I deal with are hobbled by poorly performing ductwork
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
03 May 2012 11:36 PM

Initially, I was very concerned with low register temps (88 to 90-ish),
but after three seasons, I've forgotten where the supply registers are.
The house is draft-free, and I'm not aware of any location where the
"tepid" heating air blows directly on the carbon units.

OTOH, in cooling mode, I'm acutely aware of the improved comfort.
The old air-source A/C blew freezing cold air from ceiling registers
in the bedrooms. The geo uses the (now forgotten) floor registers,
and it's nearly impossible to tell whether the A/C is running -- but
the thermostat sez the indoor temp is within 1° F of setpoint.

...one thoroughly happy camper,

Looby

One measurement is worth a thousand expert opinions.
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
03 May 2012 11:45 PM
Proper register placement and vane angle adjustment are both ill-appreciated aspects of HVAC design and commissioning.

It ain't rocket science - the basic idea is to have supply air "attack the load" which generally means directing supply air at windows and exterior walls while not subjecting occupants to drafts.

Floor registers are not normally ideal sources of cooling air but can function well if properly installed.

90-ish air works fine for heating if care is taken to avoid drafts. Supply air entrians and is diluted by room air, a fact that can work for or against the installer, depending on skill.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
ICFHybridUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:3039

--
04 May 2012 12:50 AM
It ain't rocket science - the basic idea is to have supply air "attack the load" which generally means directing supply air at windows and exterior walls while not subjecting occupants to drafts.
Is that the best way from an energy efficiency point of view?

Directing warm air right at a window significantly increases the deltaT across the weakest thermal barrier in the room.

It also thoroughly disrupts any air barrier that could possibly form at the glass/room air interface. Air barriers actually contribute to the insulating abilities.

I can see how this might possibly provide for more comfort, but, assuming that people didn't have the backs of their necks directly beneath the window, maybe you'd be better off directing the vents to mix up the air in the room. That way, the windows would "see" an interior temperature closer to room temp as opposed to the 90 degree temp of the incoming heat stream. Less overall heat loss.
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
04 May 2012 07:48 AM
Comfort systems have been designed to attack room loads since steam radiators were first placed beneath windows.

The comfort derived reduces drafts and allows occupants to save energy with milder setpoints.

This dialog may contribute to others' suspicions about your possible lack of field experience in these areas.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
04 May 2012 08:24 AM
Posted By engineer on 04 May 2012 07:48 AM
This dialog may contribute to others' suspicions about your possible lack of field experience in these areas.
Too subtle. 

Don't forget that ICFHybrid claims to be an engineer with many houses, so he MUST know what he is talking about. 
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
ICFHybridUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:3039

--
04 May 2012 09:00 AM
I suppose there are a number of strategies that might increase comfort at the expense of efficiency. Oversizing comes to mind.

Is this one of those strategies?

Your theory that it allows a reduced setpoint is interesting, but what about total energy consumption? Any data that might support that?

Don't forget that ICFHybrid claims to be an engineer with many houses, so he MUST know what he is talking about.
Geome, your penchant for making personal attacks where you should address the discussion at hand is well documented. Maybe you should stick to commenting on the material. Unless, of course, you've run out of substance or ability to be more objective. Personal attacks are not wanted here.
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
04 May 2012 09:42 AM
Posted By ICFHybrid on 04 May 2012 09:00 AM

Don't forget that ICFHybrid claims to be an engineer with many houses, so he MUST know what he is talking about.
Geome, your penchant for making personal attacks where you should address the discussion at hand is well documented. Maybe you should stick to commenting on the material. Unless, of course, you've run out of substance or ability to be more objective. Personal attacks are not wanted here.
ICFHybrid, a personal attack, really?  You have stated many times that you are an engineer, have many houses, and that you know of what you speak based on this.  Your own words - not mine.

A comment on the material?  Ok, let's take radiant floor heating.  Tubes are often spaced more closely together under windows.  I suppose that's wrong as well in your mind.  Yes/no?
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
ICFHybridUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:3039

--
04 May 2012 10:11 AM
I suppose that's wrong as well in your mind. Yes/no?
I'm not as worried about value judgements as you seem to be. I think the question at hand is whether it supports energy efficiency or not.

A stream of air directed at a window might be what, in the 90's? I don't think tubes in a radiant floor generate anywhere near that sort of temperature differential at the window.
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
04 May 2012 10:24 AM
Regardless, the principal is still the same with the radiant tube spacing.

Most people would agree that what's most energy efficient is not always the most comfortable.
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
ICFHybridUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:3039

--
04 May 2012 10:47 AM
Regardless, the principal is still the same with the radiant tube spacing
No, I disagree with your contention that the "principle" is the same, for the reasons I stated, primarily magnitude. Can I assume that you have no further data about whether it contributes to energy efficiency?
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
04 May 2012 11:17 AM
Any one who has seen a floor register knows it does not direct air straight in front of it but rather either side? Further a rom with supply and return will mix air regardless of location. Another important reason registers go that by windows is that furniture is likely to go there so those in the know.......
at the end of the day every delivery system has comprimises.

among things not wanted by me here are amatures seeking every oppurtunity to challange a pro's opinion with pet theory de jour.
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
ICFHybridUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:3039

--
04 May 2012 11:33 AM
among things not wanted by me here are amatures seeking every oppurtunity to challange a pro's opinion with pet theory de jour.
See, and I was thinking that one of the nice things about those not working in the trade was that we are willing to ignorantly challenge long standing beliefs like directing air streams at windows and the suitability of radiant and passive solar.
at the end of the day every delivery system has comprimises.
So, is it your position that directing air streams at windows is more a matter of expediency and not so much one of efficiency?
Another important reason registers go that by windows is that furniture is likely to go there
Okay, I'm a bit unclear on that. Registers go by windows because furniture goes there, too?
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
04 May 2012 12:04 PM
Directing the air flow at windows makes comfort & window-condensation sense for low performance windows with U values north of U0.34, but adds practically zero advantages with U0.25 & lower windows.

Adding a hard-coat low-E storm window over a U0.34-U0.6 double pane adds more comfort that siting the duct under a window, and is one of many efficiency upgrades that is usually more cost effective than extra geo tonnage to cover the heat loss difference for the lower performance building envelope.

With >=R20+walls and <=U0.25 windows even point-source heating works well, and it hardly matters where registers are located, leading to shorter duct runs.

Comfort is just one reason why I prefer highest-efficiency building envelopes over highest-efficiency heating systems.

But clearly, not being in the HVAC biz I have no idea what I'm talking about (ever!) :-)

ICFHybridUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:3039

--
04 May 2012 12:19 PM
leading to shorter duct runs.
So, it sounds like some efficiency could conceivably be gained by not extending duct runs just for the purpose of siting at a window?

for low performance windows with U values north of U0.34, but adds practically zero advantages with U0.25 & lower windows.
I presume that for values in between, the advantage is appropriately indeterminate?
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
04 May 2012 02:24 PM
Posted By ICFHybrid on 04 May 2012 12:19 PM
leading to shorter duct runs.
So, it sounds like some efficiency could conceivably be gained by not extending duct runs just for the purpose of siting at a window?

for low performance windows with U values north of U0.34, but adds practically zero advantages with U0.25 & lower windows.
I presume that for values in between, the advantage is appropriately indeterminate?

Depends on climate, average winter temps, etc. In US zone 7 maybe that needs to be modified to "U0.20 & lower windows".  In zone 4 and the warm edge of 5 U0.30 windows don't have much condensation potential and are quite comfortable to sit next to.

The whole radiator-under-the-window thing came about at a time more than a century ago, when windows were single-pane R1.25/U0.8 (on a good day), and leaked considerable air, and the whole-wall performance of most homes was under R5. 

The interior surface temp of a single-pane at 0F outdoor temps is pretty close to freezing, without the radiator/duct placement under the windows you'd get copious condensation or frost.

An R2/U0.50 window has an interior surface temps of  mid 40s to 50F @ 0F outdoor temps- not frost-forming, but still not so cozy.

An R3 window (U0.34, about the performance of a low-E storm over an antique double-hung in good repair, or a low cost "purty-good" low-E replacement window) is already a big improvement on comfort, making the argument for placing the ducts or radiators under the window far less important than it was in 1890.  The wall R of most uninsulated solid masonry houses is less than R3(!). The interior surface glass temp is in the low-mid 50s @ 0F outdoor temps.

At R4 (U.25) the benefit is fading fast.  Even at 0F outdoor temps the interior surface of the glass is ~60F+, and if you have an uninsulated unheated basement/crawlspace the floor could even be colder than the window.  If your mean January temp is +15F, or higher (like most of the US) there are no comfort or condensation rationalization for placement of heat sources under windows.

At R5 (U0.20), fuggedaboudit- that's a better insulating value than the whole-wall-R of most pre-1950 stick-framed houses. If you're sitting by the window at night when its -25F outside you'll still notice, not so much at +10F.

geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
04 May 2012 05:13 PM
Posted By ICFHybrid on 04 May 2012 10:47 AM
Can I assume that you have no further data about whether it contributes to energy efficiency?
ICFHybrid, you seem to assume a lot.  Where is ANY of your data?

Dana, from what you have posted, it seems as though a vent (supply register) near a window could be beneficial under the right circumstances.  If not beneficial due to windows with an appropriately high U-value, does it then make a difference if the vent is near a window, or not?

Of course, drafts can also be caused by air leaks around any window if it is not installed/sealed properly, even in new construction, so vents near windows could be beneficial.

Having vents near windows could also reduce duct length (i.e. not having to extend ducts beyond windows.)
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
04 May 2012 05:46 PM
With high performance windows and moderate-R walls the placement of either supply or return duct registers relative to window locations shouldn't much matter from a comfort point of view. Placing the return near a window may ensure that the coolest air in the room is what's headed for the HX, but the temperature differences near the floor anywhere in the room with R20+ exterior walls and U0.25 or lower windows won't be huge. Maybe directly under a very tall window it might be worth it, to vaccum up the convecting cooler air. But still, with the window surface temp above 60F in a 70F room you won't get the gusher-cascade of falling cool air that you might otherwise see with a much colder U0.6 window.

But the supply/return register locations relative to each other of course does matter.
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
04 May 2012 06:49 PM
My bad shouldve said furniture isnt likely to block widows. That said you'd be suprised how often consumer v hvac pro determines placement and even design.
Delivering adequate cfm to a room in even a new code minimum house with a ecm blower goes a long way to evening out temps.
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
06 May 2012 10:28 PM
Perhaps I was misunderstood. I certainly do not advocate placing supply ducts directly over windows, rather I have them set well back into the room so that the air stream travels over occupants heads, entrains air near ceiling, and pushes the whole mass down along windows, outside walls and doors.

Of course, being in a cooling-domiinated climate, I favor supplies and returns in ceilings. Two bonuses derive from that - furniture placement is relatively less of an issue, and high returns pick up less floor debris and animal hair.

I do favor positioning registers under windows in cold weather climes, although Dana's points about ever-better building assemblies and components make sense. One can worry less about point loads and more about merely circulating the air. Merely circulating the air becomes steadily or challenging as loads, system capacity, and airflows steadily drop on a conditioned square foot basis.

I'm not sure if ICF is unaware or being deliberately obtuse, but air from a supply register directed tangentially along a window neither impacts the glass directly nor fails to entrain surrounding air.

Oh well.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
ICFHybridUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:3039

--
06 May 2012 11:52 PM
I'm not sure if ICF is unaware or being deliberately obtuse, but air from a supply register directed tangentially along a window neither impacts the glass directly nor fails to entrain surrounding air
Of course. I was just responding to where you said;

"It ain't rocket science - the basic idea is to have supply air "attack the load" which generally means directing supply air at windows and exterior walls while not subjecting occupants to drafts."
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
07 May 2012 11:39 AM
Posted By joe.ami on 04 May 2012 06:49 PM
My bad shouldve said furniture isnt likely to block widows. That said you'd be suprised how often consumer v hvac pro determines placement and even design.
Delivering adequate cfm to a room in even a new code minimum house with a ecm blower goes a long way to evening out temps.

True, dat!  Continously variable air speed is THE standard for comfort in any air-delivered heating.

Have continuously variable ECM drives become most common sort of air handlers used  in GSHP systems, or is it mostly 1 or 2 speed?
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
07 May 2012 11:15 PM
you almost have to go out of your way to get a PSC motor in geo anymore.
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
08 May 2012 07:57 AM
I can't imagine bying geo with a PSC blower.

PSCs are pretty much reserved for code minimum air source systems these days
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
08 May 2012 09:29 AM
The price of an OEM replacement for a variable speed blower is quite high so if I have folks looking at furnaces for a modest sized home and they have no air flow complaints, we will use psc's there, but I don't remember the last time I sold one on a geo.
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
08 May 2012 02:19 PM
Posted By Dana1 on 07 May 2012 11:39 AM
... Have continuously variable ECM drives become most common sort of air handlers used  in GSHP systems, or is it mostly 1 or 2 speed?

For my WaterFurnace 2-stage ECM variable speed Envision units, circa 2007, it's in between "continuously variable" and "1 or 2 speeds."

For my 3 ton unit with 3 zones, blower speed is one of 5 pre-selected speeds.  Actual speed chosen depends on tstat settings for all 3 zones combined, using the algorithms programmed into WaterFurnace's IntelliZone zone controller unit.

For my 5 ton unit with no zoning (one tstat), blower speed is one of 3 pre-selected speeds.

Parenthetically, in a zoned situation, WF's IntelliZone produces a pulse width modulated signal to control the ECM blower fan's speed.  So, theoretically, someone could build an alternative controlling unit that supplies a continuously variable PWM signal, to achieve an 'out of the box' continuously variable ECM drive.

Best regards,

Bill

 
Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
08 May 2012 03:26 PM
Posted By a0128958 on 08 May 2012 02:19 PM
For my 5 ton unit with no zoning (one tstat), blower speed is one of 3 pre-selected speeds.
Same with all single zone Envisions -- three pre-selected speeds, and one of
those is only active for a few seconds on startup. The other two speeds are
hard-associated with the compressor mode, one each for stage1 and stage2.

Although the motor is capable of "continuously variable" operation, it's not
at all clear (to me) what benefits that might offer. Specifically, if I wanted to
design a '"smart" (single zone) fan controller, what logical rules should it
follow? What conditions would call for varying the fan speed -- other than
compressor switching between stage1 and stage2?

...just curious,

Looby

One measurement is worth a thousand expert opinions.
mtrentwUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:128

--
08 May 2012 08:44 PM
@ Looby. I'd definitely think to correlate lower speed blower with higher humidity to wring more out of the air.
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
08 May 2012 11:08 PM
Hi Dana:
You have AGAIN managed to not discredit, nor berate a theory or practice or slight the experience or past of a practitioner (other than that blasted word 'tepid' which means 88-90 for of any and all post-postings too per/of and by my references).
Alright all:

So I can now better-see an example of what I can reword about an original question:

At a fixed 90F- about ENERGY at a mini-s's  (or any on-high heat with an air speed -any 20+seer Air-Ht-Pump, but in the heating  cycle)---
 variable speeding to a slowing of air VOLUMES (I suspect just about a total thermal energy (Ex)  out===) now again- at (if we could) a fixed 90F,
and a GT also at a fixed 90-out=== (Ex)
if we could see all,
----
what would the Ex be on a SAME compressor in each tested, as the ambient outside drops from 47  to average humid  mid PA area 12-to 10F above, that I am asking: what % ROUGHLY would  the GT out-perform possibly ( est: around that 5800-6000 HDD in normal peaking -3 to-5 winters) ?

Is there an outside temperature curve ?
Is ther a related curve where someone can get a comparison?
Ducting was referenced as 'no-loss' in the house interiors where energy is received, like just Ex floating in joists areas about the duct tubing, not lost to much at all.

2) Today a manufacturer gave a verbal about how a humid Cincinnati winter temperature of at 15 degrees outside ambient could really be very near the limit for a most usable 16 SEER high speed - 20 SEER low speed mini Air Ht Pump. They mentioned dry winter times may work to 5 above for EX of but below 60% of a 47F rating. -all indoor air controlled outlet temperatures the same , just the blowers slowing down, yielding less EX output.

Thirdly ( I dare comment )
I have read of why the slick skin of an aircraft is NOT slick at lower speeds of below 60 knots like a feather is.  And that the porpoise skin is "slick" in water although straingly was rough to the touch a little bit at when I felt it. What I remember is a discussion of the 'sticky' laminar 'fluid dynamics' of air that is  also in ducting discussions about inside air layers on the inner walls of the metal during use . In solar collectors I ask about in another post, it was seen a 3/4" gap specification between top solar glass and a clear barrier to a collector. With ceiling fans I am told to not disturb the hot ceiling under the roofs or under the attic areas and to leave those fans off while cooling.
I ask about this too: Do the mini's and console units blow ON the walls? I have seen that done in pool areas about condensate, and on some very low air flows directed to sky light windows at times many years ago.
Isn't it such a like-situation of that in  a physics of all considered- if we move air more than not, and about and across a flat plate heat exchanger we will then move just more Ex?
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
09 May 2012 10:44 AM
knotET,
your ramblings are getting longer and more incoherent with every contribution. why not try short and sweet.

btw if Dana has an axe to grind it's about insulation first heat plant second. characterization of anti geo simply shows ignorance to the body of work.
j
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
09 May 2012 12:04 PM
Posted By joe.ami on 09 May 2012 10:44 AM
knotET,
your ramblings are getting longer and more incoherent ...
Hmm...

- Final rant storm from gtjp: 28 Apr

- One day rant fest by GEOjp: 30 Apr

- First appearance of knotET: 01 May

"24 hours in a day, 24 beers in a case. ...Coincidence?"
- Steven Wright

One measurement is worth a thousand expert opinions.
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
09 May 2012 03:18 PM
is there a graph of that I am asking about, leaving all that long duct commentary behind, just an answer to a first question?

Dana does not seem to be "grinding" anything, as he shared "not up close" , that I did understand.
Do you have helpful answer?

what is  is it was a question.

Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
09 May 2012 04:31 PM
Posted By joe.ami on 09 May 2012 10:44 AM
knotET,
your ramblings are getting longer and more incoherent with every contribution. why not try short and sweet.

btw if Dana has an axe to grind it's about insulation first heat plant second. characterization of anti geo simply shows ignorance to the body of work.
j

I'm definitely not anti-geo.  I'm  anti-overbuying, and prefer to see the money spent where it buys the most comfort & efficiency for the money. Sometimes that's geo, but given the low average envelope performance of the existing single family housing stock many times the money is better spent on the building.

To be clear, the higher comfort of a building-upgrade + ASHP solution has nothing to do with the temp of the heating air delivery- it has everything to do the higher-R/lower-U building envelope, with it's warmer walls, windows &  floors, and essentially no drafts.

In my neighborhood ground source heat pumps cost something on the order of 9 grand/ton for 3 to 5 ton systems (and sometimes more.) In many retrofits it's cheaper to peel off 25%-30% of the heat load with judicious envelope upgrades than it is to buy the marginal increase in geo it takes to support the higher load.  In homes under design or in homes undergoing major renovations a 50% or greater reduction can be often done on a more cost-effective basis than buying bigger geo. The life cycle of most building envelope components are on the order of a century (with the exception of ultra-high performance windows) and the operating & maintenance costs of that "missing geo" is effectively zero, so even if you're paying 10-12 grand/ton in load reductions via envelope improvements, it may still work out better in a 25 year net-present-value analysis, and better still on a total lifecycle cost basis.

When loads can be reduced to the 2 tons or less range, higher efficiency ductless air-source heat pumps (with inverter drive & variable refrigerant volume) becomes a viable option for US climate zone 5 or lower. The state of the art has improved dramatically over the past decade, rising from HSPFs in the 7s and very low 8s now hitting the 10+ range.  This makes them efficiency-comparable with geo in US climate zone 4 or lower, if still lagging in zone 5.   It's fair to say that I'm bullish on the dramatically-improved ASHP technology where it can be applied, given it's comparatively low cost (and low design risk) compared to 1-2 ton geo.

Even in cooler climates where it's efficiency is in the mid to high 2s as opposed to mid to high 3s, the cost delta may not always be worth the higher efficiency.  In Sweden, which now has building codes based on energy use performance rather than prescriptive R & U values, air source hydronic system sales have boomed, swamping geo sales (with quite a range of offerings compared to what's available N. America). But when simulated and tested in a Swedish climate (and in-situ) they're still only running seasonal COPs in the 2s.  With performance based energy use codes, the pressure is on the envelope & systems designers to come up with lowest-cost solution that actually delivers the energy use performance (there are penalties for building non-compliant buildings.) See: http://www.energimyndigheten.se/Glo...gram_1.jpg 

Geo is far from dead in Sweden, but it's market share has shrunk to something like 20-25% of the market, whereas a dozen years ago GSHP numbers dominated (and this is despite a subsidy for GSHP, though not as rich as the US subsidy.)  If it were cheaper to build a crappier house and go with bigger more efficient geo, you can safely bet the market share of heat pump type would be flipped the other way.  Hydronic air source heat pumps are not cheap either- 2x the cost of air-to-air ductless, but cheaper than GSHP, and lower-risk. Southern Sweden's Baltic-tempered climate is comparable to US climate zone 5 for winter temperatures, but much cooler in summer. Northern Sweden's winter temps are more like US climate zone 6, yet air source dominates the market.

Better grade air-to-air ductless tends to beat the average in Swedish performance table for hydronic ASHPs in climates as cool as Stockholm/Uppsala.  This has been measured both in labs and in-situ over many installations in eastern WA/ID for a program run by the Bonneville Power Administration.  While in some of US climate zone 5 regions the in-situ COPs were averaging 2.4-ish, the BPA analysts conjecture it that this was due to a preponderance of slightly older units with lower HSPFs in that sub-region, a reasonable guess given that the average in other regions of comparable or cooler weather were averaging above 2.8 with newer-model, higher HSPF mini-splits.  The numbers of units monitored in-situ are still pretty small, but it's not onesie-twosie type data with possibly large measurement error.  In the US marine zone 4 regions in the study the measured in-situ COPs were over 3.  See the metered COP column of Table 33, p.50 (p.63, in .pdf pagination).  A map of the sub-regions in that table can be found on p.8 (p.21, pdf pagination.)  Basically, everything east of the Puget Sound & Willamette is US zone 5 (with a very few installations in zone 6.)

The final report for the NW Ductless Project is due out in July of this year, but I doubt that anything in it would dissuade me from the notion that in US climate zone 5 often (but not always) better to take the first $25K of the $35K one might otherwise spend on 4 tons of geo and use it to reduce the load to something like 2-2.5 tons, then spend the remaining $10K on a 3-4 head 2.5-3 ton ductless.  The tighter higher-R building is more comfortable and durable than the higher-efficiency GSGP solution, and the annual power use is comparable.  This solution isn't always going to be possible or practical- I'm not expecting GSHP to disappear any time soon (quite the contrary), but at the same time I expect to see a surge in high performance ductless installations, as well as deeper energy retrofit upgrades on buildings going forward.

In zone 5 New England at current prices, displacing propane use with ductless pays for ductless in about 3 years even with 15 cent electricity, even assuming a lowly average COP of 2.5.  With oil heated houses it pays for itself in 5.  This is where I would expect the market to start driving installation numbers locally, but consumer awareness isn't fully there yet, just as it isn't in the Pacific Northwest.  (Ductless accounts for ~90% of the home heating market in Asia, where home sized and heating loads are smaller than in the US.)

We're still looking for that high performance ASHP forum, eh!
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
09 May 2012 09:51 PM
SO Dana thanks again:
if I am getting a 44% savings over condensing propane, with hi mass slab radiant or same type of forced air heating with GSHP multi staging, heating MODULATING blower keeping 92 or 96F outputs, what would you throw out as a % savings with mini's?
THere are no duct losses in the equation. Right statements can be accessed about ducting, but there are none in this event.

I found the graph as a table of results of the nearly 5 years of BristolCompressors.com v-Star, IQ ver rfg which is now IN GSHP for sale 60-days ago with same modulating heating blower- by temperature controls by sensor in blower cabinet. The results appear to be a 4 ton mini works like a 3.3 ton GSHP at a humid 15 deg ambient (under PA by lake Erie winter) and does barely hold CP above 2 for the ver rfg mini vs 3.4- 3.6 ALL PUMP (one) inclusive 180 w COP's of the GSHP on a needed load of about 40,000 btuhs at that 15 deg ambient. If that research holds the mini= ver-rfg AHP with propane cycling on at 7 degrees to 10, throughout to average 0-deg winters, would comparatively save about only 22-27% on the dollars, that GT is saving well over 44%. now add HW budget, and related, seems to leave still GT at ROI's over 8 years in that example at about 65oo/ton installed here, for 100% HW and GT ahd the ver rfg IQ... the dual compressor would have a quicker ROI but less dollars in 12 years savings est.
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
09 May 2012 10:39 PM
Eh! You are absolutely right, ASHPs have made a big leap forward. And they are a great bang for the buck. But you get all excited about COP in the mid 2s to 3s, when we are at COPs in the mid 4s with GSHPs, including the 230 watts for the loopfield circulator averaged over the season. So a small load in a big room, sure, mini splits are a good alternative. But whole house heating still needs a distribution system. We have to keep the comfort in mind here too. Don't you want other rooms heated, too? Once you have to put one high wall unit in each room, the cost goes up. Sure inverter technology is a big leap forward, that is why they are getting introduced in GSHPs.

Your posts on the subject are very long, and very repetitive!
www.buffalogeothermalheating.com
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
09 May 2012 10:44 PM
deleted double posting
www.buffalogeothermalheating.com
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
09 May 2012 10:55 PM
Posted By knotET on 09 May 2012 09:51 PM
with hi mass slab radiant ... what would you throw out as a % savings with mini's?




What makes you think that high mass radiant is in any way associated with energy savings?
www.buffalogeothermalheating.com
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
10 May 2012 08:34 AM
I agree with docjenser. While large radiators have some benefit (lower supply temps), high mass radiators cause overshoot, undershoot and interfere with setback. So likely to increase energy bills.
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
10 May 2012 08:39 AM
Thank you Dj,
  'high mass'  to savings?

SAVINGS,  A)  &  B)  - Above what's missing is a two paragraph explanation. - these are for your answer- my curt format:) What I leave out is for others to be  asking about later,  -not misunderstanding your Q, I believe.

A)
the only high mass I was considering was slab in-floor radiant heating - thermal Energy flow Ex:to KWH's.
This was considered with an 88F LW to 82F EW returning from load 'reservoir'-heat-sink, and about a Refrigeration-HtP system called W:W mode GT, or even to include Raypak, Rheem, Aquacal, and POOL PAK, DEKTRON, DESERTAIRE...HW-heating to heat POOLS, too. [high mass HERE: large body of heating capacity, for comfort, -just being heated, and its heat-content allowed to warm people.]
All above was just about OBSERVED, metered  lower-KWH's allowing the GTHP Ex, thermal energy to move INTO that kind of (my thought intended) a 'high-mass' releasing Ex, kinetically from , say a concrete slab floor BUT -at a steady state- of Ex (floor not changing temperature at its surface) to be considered adequately heating a space.Also, technically, as with a mixing valve for bare slab floors in a 74-82F range of those EW settings in radiant to a basement rec or play room (or with a relatively thin floor pad).
-----
B)
 The savings is relative to  ~ 4gpm per HW ton for keeping W:W below an approx. 6F Tdiff
1- At a 104F LW from the W:W mode about 8% to 12% more KWH read 33.4 amps, as a mark here.
2- COMPARED to at only 88 to 92F LW, as the compressor discharge temperature and head pressure is lower, saving KWH's reading just 30.7 amps [edited  - for not having 2) PL55B&G kw, included,- the 28.9 is Forced-Air Heat mode, EA 2340cfm at 71F ]  at that same location and system and conditions switching from low mass flooring at joists to the slab zones.

3- not me, but only that fossil fuels nox gas emissions EPA report of 1993 comparing AirHtP SEER 14 and GTHP 26 SEER at then 34%-42%, "saving" , co-relatively, was accurate about rightly seeing TODAY  IQ Ver-Rfg savings of ~ 12% today's AHT-P (no duct losses)  over nGas and close to 22% SAVINGS by GTHP [ now add HW savings, and add a low recirculated HW for radiant designed-SAVINGS, etc., heat-recovery and within and among multi-zoned GTHP ] which supports a (here in town's forum) AiqHTP saving 22% to 27% over propane while GTiqHP is saving over40%, easily... (add the cooling savings of large loop or open well GTiqHP).
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
10 May 2012 02:47 PM
Posted By knotET on 09 May 2012 09:51 PM
SO Dana thanks again:
if I am getting a 44% savings over condensing propane, with hi mass slab radiant or same type of forced air heating with GSHP multi staging, heating MODULATING blower keeping 92 or 96F outputs, what would you throw out as a % savings with mini's?
THere are no duct losses in the equation. Right statements can be accessed about ducting, but there are none in this event.


I recently ran the numbers for someone on an 80% efficiency propane wall furnace vs. a seasonal average 2.5 COP ductless using the 5-year average for MA propane & electricity pricing, and it was just shy of 60% cost savings. (Both propane and electricity are more expensive here than in OH.)  And that was assuming the propane wall furnace was providing ~10% of the heat (for backup during highest-humidty cold & peak lows.)

So with condensing propane assuming no duct losses that would be about 50% savings.

[edited to correct]

I was misremembering.  Looking over the analysis I submitted the savings at the 5 year average propane/electricity price with 90/10 division of ductless/propane heating came in at 46% savings.

It was at the 2011-2012 rates that it came in at 59% savings.

Total heat load where-is-as-is for this small place (about 800' of conditioned space) was still under 30KBTU/hr. I recommended some insulation & air sealing upgrades, and low-E storms over the remaining single-panes, of which there were two, and going with a 2-head 2.5 ton ductless which would be about a 90% solution. The balance & comfort would be better than the wall-furnace + space heater she's been living with, and the upgrade package (including the ductless) would pay off in under 6 years (simple) using the 5 year average, under 4 at last year's rates.  If the ductless performs at a COP better than 2.5 (which it should) it'll pay off sooner.  There is no GSHP solution that would fit her (retired, living pretty much on social security) budget, but the sub-$10 investment recommended will do much better than where her savings had been parked.
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
10 May 2012 04:20 PM
Posted By docjenser on 09 May 2012 10:39 PM
Eh! You are absolutely right, ASHPs have made a big leap forward. And they are a great bang for the buck. But you get all excited about COP in the mid 2s to 3s, when we are at COPs in the mid 4s with GSHPs, including the 230 watts for the loopfield circulator averaged over the season. So a small load in a big room, sure, mini splits are a good alternative. But whole house heating still needs a distribution system. We have to keep the comfort in mind here too. Don't you want other rooms heated, too? Once you have to put one high wall unit in each room, the cost goes up. Sure inverter technology is a big leap forward, that is why they are getting introduced in GSHPs.

Your posts on the subject are very long, and very repetitive!

I've not seen credible 3rd party data to support the notion that the average full system GSHP seasonal COP is in excess of 4 yet, despite the onesie-twosies at the 2 sigma margins.  But if you can show me where to find third party survey data on instrumented & monitored systems such as the dozens of mini-splits in the NW Ductless project I'd be very interested to look at it. The smaller-scale studies I've seen to date all point to mid-3s as the system average. (Mid-3s, as in the measured average performance of a fleet of 1-3-ton mini-splits in Seattle.)

A 3-head 3 ton ductless can handle quite a lot of house floor plan configurations for under $10k.  And in a high-R home the room to-room temperature imbalances are pretty small compared to an R13+5 / U0.35 code-min type of house.  The notion that you would need anything like "...one high wall unit in each room..." to keep the place comfortable simply isn't well founded, even in a code-min house (but you may have to boost the temp a couple degrees in the rooms with heads to keep those without comfy at design temp in a code-min house.) High-R houses are far more amenable to point-source heating than typical construction, and the "...needs a distribution system..." argument fades pretty fast and pretty far- to the point where a well thought out HRV system can be used to further balance the temperatures (as is being done on a local deep energy retrofit I'm advising on.)

Marc Rosenbaum has been heating his moderately high-R house in MA with a single head 1-ton Fujitsu, and has been monitoring the temperature in different parts of the house. His too was a retrofit hack in a house not intentionally designed for  point source heating, and does not use the HRV design to balance the flows, but his room to room delta-Ts weren't terrible, and the cooler lows could have been better had he been willing to turn up the temp (something he is loathe to do, unlike the typical homeowner.)  His house does not have PassiveHouse type R-values (not even close) but as-operated it's pretty much net-zero, with 5-6KW of PV on the roof and an energy-stingy lifestyle of the occupants. But they're not freezing their butts off in one room and roasting in another.  The mini-split cost less than the nearly-new Buderus boiler he hauled out shortly after moving in.

The excitement isn't COPs in the 2s & 3s per-se it's the prospect higher comfort of the higher-R envelope  at  similar upfront cost (and operating cost) of the GSHP-only solution for achieving the same operating cost.  A COP of 5 would be pretty exciting, but not so much if the system cost was $150K.  At $9K/ton for a better class GSHP running a system-COP of 4 won't always make up for the cost difference between COP-3 ductless at $2.7K/ton during it's lifecycle, even if you add ton more ductless for low-temp capacity.

At the warmer edge of climate zone 4 don't be so sure that GSHP installations would always beat a better class ductless on raw efficiency either.  At mid-compressor speed they're all above 4.0 at 45F outdoor temps, and at low speed they're even higher.  To have sufficient capacity to handle the load at a design temp of say, 25F (where it's running with a COP of 3 even at high speed) it'll be just idling along at at winter average temps of 45F, with a COP in excess of 4. In the NW Ductless monitoring the measured average COP in the Willamette region (a middle-temp part of zone 4) was in the 3s. (See table 33.) Design temp for Eugene OR is +26, Portland is +24 but the Puget Sound cluster has a comparable or cooler design temps and averaged in the mid 3s. Raise the temp 5-6F on the high slope part of the curve and it make a half COP difference.  Oversized by 25% at design temp and that too makes about a half-COP difference.  The vast majority of the units tested in the NW Ductless project were not intended as whole solutions, and as such were probably running slightly higher average compressor speeds for lower average efficiency.  These were for the most part retrofit-hacks into sub-code-min houses, not whole-solutions to well designed higher-efficiency building envelopes.


The varible refrigerant volume ground source technology is also pretty exciting stuff, but the total bang/buck of the whole house, not just the mechanical systems is more interesting to me than any "gee-whiz" mechanicals, and when the mechanicals are expensive, it pays to do the math on the balance point between higher efficiency building envelope vs. higher efficiency mechanical systems.  Moderately high-R is pretty cheap, when designed in from the start.
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
10 May 2012 10:53 PM
Posted By Dana1 on 10 May 2012 04:20 PM
Posted By docjenser on 09 May 2012 10:39 PM
Eh! You are absolutely right, ASHPs have made a big leap forward. And they are a great bang for the buck. But you get all excited about COP in the mid 2s to 3s, when we are at COPs in the mid 4s with GSHPs,... Sure inverter technology is a big leap forward, that is why they are getting introduced in GSHPs.

[ knowing a little of the author of this thread tries to be accurate ] Dj states: Your posts on the subject are ...  repetitive! [ do you also mean DANA1? It is not clear to this author ]

DANA1 stated to Dj:
a)
I've not seen credible 3rd party data to support the notion that the average full system GSHP seasonal COP is in excess of 4 ----

b)
----one high wall unit in each room..."
to keep the place comfortable simply isn't well founded,

c)
willing to turn up the temp ----
---
The excitement isn't COPs in the 2s & 3s per-se it's the prospect higher comfort of the higher-R envelope  at  similar upfront cost (and operating cost) of the GSHP-only----
At the warmer edge of climate zone 4 don't be so sure that GSHP installations would always beat a better class ductless on raw efficiency either.

d)
The var-refg//---[as to] Moderately high-R is pretty cheap, when designed in from the start.

Dana
only annual 4.1 held by TETCO from 1979, having 5-t  60k HX on 43k compressor (like a mini- 4.1/2 "ton" for today's comparrisons) it was an early stage  - among multiple units running from thanksgiving to easter , non-stop. This had a near 7-real ton air coil and at the old 1/2 hp blower cap-start-cap-run hi eff GE, then moving 1650+ cfm, head pressures under 205 r22. The ONLY 410a at over-blown 500's cfm/ 10,000 btuh's usable net heat output, with head pressures below 300  and suction pressures (38-40 deg loops) above 110, are constantly nearly always over 4.0 cp's. The annual FUE -GT Ex at cp's of nearing a 4+ mark can easily be found with 100% domestic HW production in larger families of 5+ with PRIORITY-HW / annually-cycling, -respectively.
a)
AGREED ( by more of a GT nut that anyone will know for a while ) . Discussion from me did only point to, w/ little DeSuperheaters, of annually 3.4 cp's (very conservatively, though, for 2012 eStar GT-HP's). Tier 4eStar GT-   will FORCE all to either use 55% over-sized water coils on 35% over-sized air coils with minimum 2-staging systems and all that about the now selling: GTiq, as well as Aiq's. IQ by WF "due in JUNE" I was told today by a largest dealer. Hydro-Temp of AR already sells it. W:W and Priority full condensing in GT-HVAC are both going to have very little need of "buffer" tanks: iq4U !
b)
Djensen: Please keep asking; and at a point by line, with ANY commentary (always). We DO need your input regardless of some fringe commentary, politely-ment -an opinion of mine, although among MANY members that I see "long" and "repetitive" b/c of NEW THREADS for NEW VIEWERS allowing such a 'right' to welcome dozen's of thinkers to any thread... So you can CONTINUE reiterating, too, for any new thread, please:)
Dana1=
agreed again with that
  b)
When there are those who bragged of 50 MPG in a vw -as they really were a researching DIY monster-  (Dave W. , I knew in 1980...)by shutting off the engine, coasting, in a stick... - well  then any central heat source of a 10 deg warmer room at 75 in a space, to 67 in a closed door bedroom works for them. Them's are many more than I can imagines (all global humans inclusive).
c)
From of about all I have run into Dana1,
- there's a big divide between your shifting excitement of yours to imply "isn't cp's" to "...is...envelope", I have reason to be simple minded about.   I will argue at every post: Cp's are more than just one 'branch' off the trunk of the "envelope-" tree  and reach to those roots of greeni-things.  Fluid dynamics  of Ex, among the physics of Ex, thrills  most people I know that are the buyers-closed.    - This experience in 35 years of face-face seems true whether they can commmunicate it well, or can't (-or I don't.) Only highly positive responses are found about sharing just some of a 70% to 76% of sustainable ground/solar Ex discussion; or AHPiq's getting to just over 60% of that sustainable Ex, -maybe. COP explanation is met with wide acceptance. So I cannot concur a CP as discussed is being an "isn't" to a "what is" b/c of the abounding interesting positive responses. I have found CP-branches are full of many 'swings' that people enjoy riding ... Very many - right next to you in that swing.
d)
Doing 80% retrofitting- and from those "starts" = always in agreement with you there.

z)
Dana1 on another thread of a Mr miller, 1700 sq ft oil 04/12, , I believe in that kind of 425 gal of oil Sep-Mar 2012, very USUAL N-OH winter of -5 below (not Cincinnati +3 above to many -0's I lived in 19 years...in Z-Cinti) but like that even in at the boarder to wVa, those 0-deg towns in to below zero winters all seem to need more relative comparison of a more like 750-900 gal of oil in a usual winter to be expressed as ~ more of 40-48,000 btuh's .

Before the r-envelope fixes, 44,000-48,000 as the 'starting' argument. This would barely result in a 32-to-34Mbtuh design in these 7-8-12 degree balance points; and again, after practical fixes on a tighter budget as indicated. The smallest GTiq I can discuss is "size 3.0" comparing to Mini's on a 55-degree to 50-degree day Ex output. At 47F the ministarts falling off to about 15% less at 7-to-8 degrees long running cycles and GTiq is 45% higher COP, there and then.
A sales oddity is a "size 4.5" GTiq is only 600 more and a "size 5.5" only 450 more to a buyer, by just the Unitary component of the cabinetted  equipment alone. So 450-700 "gal-oil/yr-htg homes just fitting for a  "3.0" GTiq.

IN a real 55,000-45,000 load at -5 to 5 above zero load, r-envelope fixed... HERE I FIND: Pricing 5 mini zones off a 4 ton -iq appears to be for a retrofit @ $ 16,000 installed with 2 year service agreement and 5 yr parts and labor (pro-rata). < 400 Ut'y Co- rebates >...vs... $ 25,500. for a  "size 4.5" GTiq that IS a 1-winter ROI on the difference, making 100% HW, 3 zoning inclusive, and can have a little $ 175. HX coil for some Radiant or Pool spin-off. GTiq net book cost @ only $ 18,000 or 4500/ton WITH HW instant heater and tank and insulated lines and ,,,and,,, + nearly 2 1/2 times the dollars saved now in 10-12 years/ of the 30-yr longevity, and easily way more realestate value in 5 years ( at least 4 degrees above 'tepid' = fixed temp-modulating blower-sensing ) NOW.

~~~~~~~~~~~~~~~~
Aiq-HP thread is NEXT ! :)
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
12 May 2012 01:15 AM
Posted By Dana1 on 10 May 2012 04:20 PM
I've not seen credible 3rd party data to support the notion that the average full system GSHP seasonal COP is in excess of 4 yet, despite the onesie-twosies at the 2 sigma margins.  But if you can show me where to find third party survey data on instrumented & monitored systems such as the dozens of mini-splits in the NW Ductless project I'd be very interested to look at it. The smaller-scale studies I've seen to date all point to mid-3s as the system average.


http://www.builditsolar.com/Projects/SpaceHeating/InField%20PerformanceTestingofGSHP_updated%2011_11_2010.pdf

You are right, good published studies are lacking, the one above is quite bad with very inefficient systems and lots of variances, which make me question the data. We see average total system COP in the mid 4s with 3 ton dual stage W-A, with an average heating season EWT of 38F. We have 15 Welserver online, and should summarize and publish the data.
www.buffalogeothermalheating.com
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
12 May 2012 01:49 AM
Posted By knotET on 10 May 2012 08:39 AM
Thank you Dj,
  'high mass'  to savings?

SAVINGS,  A)  &  B)  - Above what's missing is a two paragraph explanation. - these are for your answer- my curt format:) What I leave out is for others to be  asking about later,  -not misunderstanding your Q, I believe.

A)
the only high mass I was considering was slab in-floor radiant heating - thermal Energy flow Ex:to KWH's.
This was considered with an 88F LW to 82F EW returning from load 'reservoir'-heat-sink, and about a Refrigeration-HtP system called W:W mode GT, or even to include Raypak, Rheem, Aquacal, and POOL PAK, DEKTRON, DESERTAIRE...HW-heating to heat POOLS, too. [high mass HERE: large body of heating capacity, for comfort, -just being heated, and its heat-content allowed to warm people.]
All above was just about OBSERVED, metered  lower-KWH's allowing the GTHP Ex, thermal energy to move INTO that kind of (my thought intended) a 'high-mass' releasing Ex, kinetically from , say a concrete slab floor BUT -at a steady state- of Ex (floor not changing temperature at its surface) to be considered adequately heating a space.Also, technically, as with a mixing valve for bare slab floors in a 74-82F range of those EW settings in radiant to a basement rec or play room (or with a relatively thin floor pad).
-----
B)
 The savings is relative to  ~ 4gpm per HW ton for keeping W:W below an approx. 6F Tdiff
1- At a 104F LW from the W:W mode about 8% to 12% more KWH read 33.4 amps, as a mark here.
2- COMPARED to at only 88 to 92F LW, as the compressor discharge temperature and head pressure is lower, saving KWH's reading just 30.7 amps [edited  - for not having 2) PL55B&G kw, included,- the 28.9 is Forced-Air Heat mode, EA 2340cfm at 71F ]  at that same location and system and conditions switching from low mass flooring at joists to the slab zones.

3- not me, but only that fossil fuels nox gas emissions EPA report of 1993 comparing AirHtP SEER 14 and GTHP 26 SEER at then 34%-42%, "saving" , co-relatively, was accurate about rightly seeing TODAY  IQ Ver-Rfg savings of ~ 12% today's AHT-P (no duct losses)  over nGas and close to 22% SAVINGS by GTHP [ now add HW savings, and add a low recirculated HW for radiant designed-SAVINGS, etc., heat-recovery and within and among multi-zoned GTHP ] which supports a (here in town's forum) AiqHTP saving 22% to 27% over propane while GTiqHP is saving over40%, easily... (add the cooling savings of large loop or open well GTiqHP).


While you continue to be not very clear in your writing, let me make a few points here:

1) The purpose of a heat deliver system is to deliver heat, not to store heat. HIgh mass is desirable in a building to a certain degree, but not in the heat delivery system, which you want to be quick responding.

2) While efficient radiant systems use very low supply temperatures, this has nothing to do with high mass, but more with their ability to conduct heat to the above floors effectively.

3) While part of the claim of radiant being more efficient has to do with the assumption that one has the same comfort level at lets say 65F radiant than forced air at 70 f degrees, studies have show that houses with radiant system do not lower their temperatures below comparable forced air systems.

4) Yes, water stores about 3500 times as much energy (heat) and the same volume of air, the distribution can be cheaper. Small circulation pump versus blower. Overall, maybe a 5% saving.

5) Radiant can still save a lot over forced air if you design your system down to the lowest possible supply temperature, making a heatpump fed system more efficient. However, this concept has nothing to do with the mass of the radiant, but, again, with efficient conduction (and a bit convection) of the heat to the above space.
www.buffalogeothermalheating.com
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
12 May 2012 10:15 AM
HIgh mass is desirable in a building to a certain degree


I say "may be desirable". For example, if you have an office building used 8 hours/day, mass may ADD to the energy needed in the morning and extend the btu losses into the evening. On the other extreme, if you maintain a steady indoor temp 24x7, indoor mass doesn't help you either.

Exterior mass is less likely to have downsides but it too "depends on the weather".
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
12 May 2012 06:05 PM
Posted By jonr on 12 May 2012 10:15 AM
HIgh mass is desirable in a building to a certain degree


I say "may be desirable". For example, if you have an office building used 8 hours/day, mass may ADD to the energy needed in the morning and extend the btu losses into the evening. On the other extreme, if you maintain a steady indoor temp 24x7, indoor mass doesn't help you either.

Exterior mass is less likely to have downsides but it too "depends on the weather".


...TO A CERTAIN DEGREE....

I am mainly looking at residential buildings here,where it buffers the solar gain nicer. In the morning it absorbs the heat nicely, takes longer to heat up during the day, and then carries that heat into the night. That buffering effect is more pronounced in heat dominated climate. But even in an office building, which is more likely to be cooling dominated, you want that building to cool during the day and store that heat during the night, so you don't have to heat it up as much for the crowd arriving in the morning, and then stay cooler during the day.

Yes, if you stop heating at 72 degrees and start cooling at 72.5 degrees, high mass does not help you much, but most people are quite comfortable between 68 and 78F, depending on humidity levels, and this is where high mass houses really shine.

The whole point was that you want the mass in the building, not the radiant system. Putting it into the basement slab is ok, since the basement does not fluctuate as much due to less solar gain, and ground coupling. I can't think about any circumstance where a high mass radiant actually increases comfort and saves you $$$ compared to a low mass radiant system.
www.buffalogeothermalheating.com
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
13 May 2012 10:33 AM
I agree. Solar input along with occupants who are willing to tolerate a wider range of temperatures is a case where passive, non radiator mass is useful. In other cases it can be a negative.

Active mass is different in that it is always helpful.
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
13 May 2012 10:50 AM
Posted By Dana1 on 02 May 2012 04:34 PM
I've only seen a handful of geo-air systems up close & personal.... but many are multi-stage. ---- [can]  minimize wind-chill from tepid air systems in McMansions, a bit tougher in a 1000' Cape style house.

-looked up 'tepid' for standard def- and always, T's D1:)
 (COMMENT BELOW IS SIMPLY NOT FOR LOAD STUDY NOR BUILDING IMPROVEMENTS) 

just look at heat pump / like low temp air solar:
cfm = half the sq ft in an 8.1/2 high ceiling res. rm.  
= coincides with about 3.1/2 air rotations [not yet just through equipment, here] air-rotations/hr  for  a corner-corner comfort.
Condition 1)
Not any more output air blowing on occupants than would a motel P-Tac wall unit or a mini-split.
Condition 2)
Not open for my time for any argument:
[about  blasted-too-near-to-surfaces = heat exchanged Ex] ONE MUST absolutely only be  leaving at-rest/alone   all unconditioned walls and glass thin boundary layer, of that INSULATING air-film, -that laminate air layer,  undisturbed at mechanical 'rest' for a least EX and a highest comfort,  "screened in front of, not on a wall as Curt (engineer)  put in his first portion of his commentary, clearly-   enough. LCFH on the way that I was thinking anyways.

Condition 3)
Technic-Picking-
With a basis about----
When the glass-radiant heat folks stormed through in 1980's at/in "gas shortage out-cry"-days, 
they left a report on "the architecture of the skin" .
 Relative to no air moving and clothed surfaces in say shirts with sleeves, ~ 74-deg  human in a slow walk or some sitting was read by infra-red scanners. Anywhere 'budding engineers' collect at drafting tables for half of a day, or high school hot headed teens , after winter sports sat in an art room in a basement-like classroom, finished walls, uninsulated, it was been found that an actual air temp of over 72 and usually 73+ on a wall stat IS REQUIRED for hands to function comfortably. (Art-Room of Picasso'ess-Pit, as a sign read at the foot of a stairwell,  Mother/Teacher there kept stat at 73 all winters 1970's)
The boys can argue (at there cost and/of moral)  all day, but the desk worker usually has more comfortable tactile mobility at 73 air about the hands.

yeah D1, engineer, Joe, and all of you , this is but  - a bit subjective,
but concept and practice carried into solar and Air and GT HtPump ducting desiging and comfort that buyers are glad to have.

100 sq ft or 1000 or 10,000...  3 to 3.1/2 air rotations effectually eliminate 'tepid' still air at ~ 78F, some slow moving at 84-86F, and 200 to 400 feet per minute from 88F-92F at out of registers in any system. [will always be my-closer-to-standard-read definition in what as I thought was 'tepid' (it has your definition with a temp , though)]
.  As you mentioned felt and we still see today- 'cool-flows' are in direct contrast to the following:

Old school 450-550 FPM air register velocities ,  unless low budget installs prevailed,  - for some HtPump installations have all but stopped with tricks of 2HT+2CL stats in the 80's grabbing multi-speed blowers wiring for "staging-like" getting 2-'stages' from single speed equipment. Artisan up-to 18 min time delays 'staged' off 1HT stats on a blower-relay addition.

 By the introduction in the EARLY '80's of 3-staging dual compressors of at 30% to 70% to 100% Ex (energy flow allowance) staging greatly improved. (Later copied by TRANE , etc. single refg coil circuiting.)
4 and 5 speed blowers were tap/wire selected for COMFORT. I only noticed in 1996, residentially programmable (tech-plug-into-board) with Pulse-Width-Modulated ECM-1 10%-100% speed selection I used on "SIZE 5.9" GTHP's of two customers .

I did find the tables of comparative MiniIQ and Daiken and GT standard to GT IQ now. (and as you seemed to figure out, was not asking about ducting, though info bites were fun reading DUCT 101 and DUCT 102, again)

DANA:
This was the Q' , you seemed to see/begin to answer,  that I had asked at the beginning:
regardless of subjective def's:
47 down to 5  (and  -5 below zero)
Graphs? Reference tables?
Regular AirHtPump, GThtPump, Mini's and IQ/VerRfg by veraible compressor motor drives ((not a whole lot different than 3-staging, 4-staging from the 1980-'s , I now see, in the field with all the swings. re: OUTPUTS to KWH Consumption, repairs, expense, etc.)) - all considered JUST AT a CONSTANT AIR TEMP output Ex does vary by --- What ? Loaded , in a room...?

I have some answers now.

knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
13 May 2012 10:55 AM
I see ~ 15% output -some cyclic-defrosting- DROPS Miini/AHPiq
[in other posts: IQ Ver RFG Air Source Heat Pump ===  Aiq  for referencing]
on high speed, fully loaded, as a 3.1/2 " ton" is then running at 5-to-10F above zero, like its rated 3-"ton" at 47F on an ISO standard charting, lab conditions. Since Parkersburg WVa to Cleve to Erie PA, all have nearly EVERY WINTER sub zero weather, just wanted to see a difference, if any different than APPLES:APPLES GT to Air Ht Pumps, today: GTiq:Aiq.

At -5, I can clearly see in humid winter areas:
 more than 30% seasonal cyclic differential in KWH advantage of GTHtP--
 compared to way oversized- to -keep up at a 7-12 deg balance points before needing supplemental heating with AirHtP, in those normal sub-zero winters.

This concurs with the 1993 EPA Nox gas emmisions studies covering Air to GT Ht Pumps in their data, highest-Eff to Highest Eff , then , and that was not compared to the heating of the COP 4.1 TETCO W:A of 1979, heating only GeoThermal. (now built by Enertech, and now Ph4 for HW and Radiant, combo, like a Hydron Combo "module" and others

That "AIR HT P forum" is up in recent posts.

Dj:
Steady-State, mass or not, I read the amps, the data was resounding, 8% to over 10% : the Forced Air GT walked away over the 104deg HW radiant at 4gpm per ton at the gt... like 88Fdeg HW leaving at 4gpm per ton to compare (USED an existing slab for test) to F Air with 72 incoming air. Let's do that analysis at another thread so INITIAL Q's get answered. T's again ! Desiging and all that good info biting is needed.



EDITED for MikeSolar-  "MS"
MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
13 May 2012 12:02 PM
knotET, I've been around this stuff for 30 years and thought I knew most of the acronyms but I really have a hard time reading your posts (I am trying really hard), but it is making my head hurt. Could you do us a small favour and use the same acronyms that are common to the others in the biz.

Failing that, make a list of some of you more inventive ones so that we can follow along more easily. Thank you.


Somewhere back in this thread it was alluded to that thermal mass is not so important in energy conservation with heat pumps and I believe Dana1 said that a masonry wall has a r-3 value. The current measurement scales have a hard time taking into account the thermal lag and flywheel effect that occurs in masonry homes. I live in a standard 3 story double brick 1800 sq ft home or 1918 vintage and my heating bills are lower than an almost any 1800 sq ft stick frame (nominal R20) home. Point being...I can't see how the point of thermal mass being unimportant is true......comments anyone?
www.BossSolar.com
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
13 May 2012 12:45 PM
Posted By MikeSolar on 13 May 2012 12:02 PM
knotET, [(kE is fine)] [kE] -brackets
 MS:
I've been around this stuff for 30 years and thought I knew most of the acronyms but I really have a hard time reading your posts [I.E.?- what's the question, or can you just private message, if you want amplification?] 

[2) Gotta answer for the Q' ?]

[3) tangent discussions of the "ducting" etc, mass had little to do eith the real Q; I believe could me given a sign post and send us to more relavant threads to those off-topic writs.]

MS states:
Somewhere back in this thread it was alluded [Politely: just  not by the Q nor the poster] RE: to that thermal mass is not so important in energy conservation with heat pumps .
 [ and that is as a separate thought to me too,  to- ]    and I believe Dana1 said that a masonry wall has a r-3 value.
 
The current measurement scales have a hard time taking into account the thermal lag and flywheel effect that occurs in masonry homes. [((true))] [but I actually touch on how , above. I will decode in another thread on that of yours. Please START a Q'.]

MS states:
I live in a standard 3 story double brick 1800 sq ft home or 1918 vintage and my heating bills are lower than an almost any 1800 sq ft stick frame (nominal R20) home.

Point being
...I can't see how the point of thermal mass being unimportant is true......comments anyone?
Thanks.

"Ex"  x mass "unimportant "  to this Q in the top of the thread, as to  Ex (Ex - is a common term for thermal energy transfer about an HX heat exchanger/. It is in wikipedia, net articles, GEOExchange, 'the Source', etc.).

HtP for Heat Pump, here; 
 please give some type = notice (What is regularly abreviated, of/to you ) on that newthread about the mass and things. 

We can move along.
-only at steady state, about Ex, was the comment about a high temp (in a low mass of plates to flooring) or low temp READ  [occuring] in a high mass, OBSERVED  Ex  device, called the basement flooring  (as at a HIGHER temp radiant [not more nor less WORK was the discussion] to the wood above). COMPRESSOR to temperature of the refrigerant was the direct concern indicated by AMP draw.

It was JUST A READING at an existing home - not a design,  nor had anything to do with ducting, - if I can but amplify for all- .

3)   interesting you mention , "in 1800" 1400 12 inch to lathe walls, 400 cape code finished above, loosely insulated split down to utility and storage next to 3 bay garage. Top 400 is closed all winter until occupied by 1 a few days.... and too, I have below average heating costs, with 2 or 3 deg more comfort! Attic needs more !

4)  a) Thread on ducting
     b)  Thread on mass and slabs and flooring  and distribution sorely needing over 104 LW radiant.
     c)   Thread on YOUR typical mass but you could help me with more pointed singular questions or anyone.

5) This thread Q's) have been completed in answers and by more research. -answered since finding articles, and now that  GTiq is here.  (GTiq: IQ GT HtP Veriable Refrigeration Drive BY a Phase inverted Brushless DC motor in a mechanical compressor for Air and Water and other applications to be distributed COMFORTABLY and EFFICIENTLY as a 'budding engineer' can feel indirectly, but humanly even for months in a womb).

4) d) Solar thread? Too, what can you ask regarding informing and to see others ideas and experiences, please...? 

docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
13 May 2012 11:27 PM
Posted By MikeSolar on 13 May 2012 12:02 PM
I live in a standard 3 story double brick 1800 sq ft home or 1918 vintage and my heating bills are lower than an almost any 1800 sq ft stick frame (nominal R20) home. Point being...I can't see how the point of thermal mass being unimportant is true......comments anyone?


You give us the best example how thermal mass is very important in buffering the heat for saving energy and comfort is.
Again, thermal mass in a building is good, thermal mass in radiant system is bad. There is a reason why 2000 years ago, or even 100 years ago, building performance was more comfortable and sometimes more efficient than today.

I lived in buildings with 2 foot brick walls for 35 years in Europe, not needing any A/C, and using all the solar gain there is to minimize heating.
www.buffalogeothermalheating.com
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
14 May 2012 12:22 AM
Posted By knotET on 13 May 2012 10:55 AM
src="https://www.greenbuildingtalk.com/DesktopModules/ActiveForums/themes/gbt/emoticons/smile.gif">

That "AIR HT P forum" is up in recent posts.

Dj:
Steady-State, mass or not, I read the amps, the data was resounding, 8% to over 10% : the Forced Air GT walked away over the 104deg HW radiant at 4gpm per ton at the gt... like 88Fdeg HW leaving at 4gpm per ton to compare (USED an existing slab for test) to F Air with 72 incoming air. Let's do that analysis at another thread so INITIAL Q's get answered. T's again ! Desiging and all that good info biting is needed.



EDITED for MikeSolar-  "MS"


Let me clarify this. If you design your radiant system as efficient as possible, meaning for a low supply temperature, your W-W heatpump can run more efficient than a W-A heatpump due to lower refrigerant pressured and higher COP. Thus radiant floors can be more efficient in heatpump applications than forced air.
www.buffalogeothermalheating.com
MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
14 May 2012 07:04 AM
The principal is the same whether ASHP or GSHP. Close up the dT and the efficiency increases. There are two ways to do this on any given house.....reduce spacing or increase mass. The only down side to having high mass in a radiant system is response time, but if the rest of the house is high mass, the temps don't need to fluctuate quickly. We have done a number of off grid houses with radiant stoves, high mass, and the temps rarely vary more than a few deg, even without supplemental heat.

I have seldom seen a reason for low mass radiant except for a builder who is not willing to wait for gypsum cement to dry out properly.
www.BossSolar.com
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
14 May 2012 11:29 AM
Posted By docjenser on 12 May 2012 01:15 AM
Posted By Dana1 on 10 May 2012 04:20 PM
I've not seen credible 3rd party data to support the notion that the average full system GSHP seasonal COP is in excess of 4 yet, despite the onesie-twosies at the 2 sigma margins.  But if you can show me where to find third party survey data on instrumented & monitored systems such as the dozens of mini-splits in the NW Ductless project I'd be very interested to look at it. The smaller-scale studies I've seen to date all point to mid-3s as the system average.


http://www.builditsolar.com/Projects/SpaceHeating/InField%20PerformanceTestingofGSHP_updated%2011_11_2010.pdf

You are right, good published studies are lacking, the one above is quite bad with very inefficient systems and lots of variances, which make me question the data. We see average total system COP in the mid 4s with 3 ton dual stage W-A, with an average heating season EWT of 38F. We have 15 Welserver online, and should summarize and publish the data.

I'd already seen that one, and it's consistent with several others. Question the data all you like, but until there's published evidence that the industry average has has moved forward from that point, I don't see any reason to believe that a typical GSHP installation are even close to averaging in the 4s yet.  In fact I haven't seen ANY third party tested system that beat 4 as a seasonal average, but I wouldn't necessarily be shocked to find an existence proof some day. Yet I tend to believe people who actually measure stuff when they have no financial interest in the outcome rather than blindly accepting vendors' spec sheets, or the marketing literature/protestations of installers.  Allegations aren't evidence.

Just as with mini-splits- the average in-situ performance of tested systems can hint at what's possible, but from the prospective buyer's point of view it's unwise to assume that you'll beat the industry average.  Best-case scenarios are rare, but of course better-studied better-designed implementations can industry averages.  Just as I wouldn't assume an average COP of 3 for a ductless in US climate zone 5 (even though I believe it's possible with an optimized oversizing factor), I can't assume an average COP of 4 for GSHP based on an installer's say-so or industry-insider lore.  \

Say whatever you like, but show me, and don't be too sensitive when others call THAT data into question.

As a crude measure of where to place expectations, in US climate zone 5, for now I put the backstop at 2.5 & 3.5 for ductless & geo respectively.  While it might be at the lower-efficiency side of dead-center on the bell curve, it's probably within a single standard deviation.  In US climate zone 4  that moves up to 3.0 and 3.5 based on the available evidence.   But the fact that average for one of the zone-4 sub-region in the BPA study was 3.4, the possibility that at least some installation in that mix was averaging about 4, seems likely while others were only 3. 

Of the two non-instrumented systems in climate zone 4 that I have first-person reported billing data on, an average north of 3 would be consistent with the power use.  A 4 average would be a bit surprising, but not entirely out of the question for one of them, but it hasn't been up for an entire heating season yet.

Note that the testers in the BPA study were unable to achieve the HSPFs published by Mitsubishi, either in the lab or in-situ, but were able to demonstrate that their lab measurements were consistent with the field-monitored performance.  But they COULD reproduce the Fujitsu-published HSPF both in the lab and in-situ.  But since Mitsubishi holds the lion's share of the installations in that study it's conceivable it skewed the averages downward slightly.  As the state of the art moves forward it should all be moving up incrementally.


MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
14 May 2012 08:42 PM
Dana1, here is a link to the IEA website on the development of the ASHP and GSHP. The report is a final one detailing best practices and in it you can find some system performance data. There are some ASHPs with COPs approaching 4 and GSHPs with COPs near5.

http://www.annex32.net/field_monitoring.htm

The difference, in my mind, between North American HPs and European units is partly one of holistic design. We tend to take heat distribution by forced air system as a given which they don't do. It is considered lowest common denominator in Europe and the floor heating or radiators is included in the building design from day one. Forced air would generally not be considered because it takes up space, is more noisy and uses more energy to move the heat than heating with water.

The people I know over there use, for example, tubing with a 4-6" spacing in concrete which can result in 30C EWT and a 5-7C dT. Very different practice from here.
www.BossSolar.com
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
15 May 2012 01:16 AM
Posted By MikeSolar on 14 May 2012 07:04 AM
The principal is the same whether ASHP or GSHP. Close up the dT and the efficiency increases. There are two ways to do this on any given house.....reduce spacing or increase mass. The only down side to having high mass in a radiant system is response time, but if the rest of the house is high mass, the temps don't need to fluctuate quickly. We have done a number of off grid houses with radiant stoves, high mass, and the temps rarely vary more than a few deg, even without supplemental heat.

I have seldom seen a reason for low mass radiant except for a builder who is not willing to wait for gypsum cement to dry out properly.


The response time is a huge issue in higher efficient buildings, which simply don't loose much heat, and usually have much solar gain.
High mass floors are taking hours to heat up and hours to cool down. They don't give you heat when you need it, and then still heat when you don't need it.
May be you can elaborate how a higher radiant mass will increase efficiency? What matters is the conduction from the pipe to the floor above. Yes, spacing is one way. Gypsum and concrete is a bad conductor, aluminum is much better.
www.buffalogeothermalheating.com
MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
15 May 2012 06:58 AM
Posted By docjenser on 15 May 2012 01:16 AM
Posted By MikeSolar on 14 May 2012 07:04 AM
The principal is the same whether ASHP or GSHP. Close up the dT and the efficiency increases. There are two ways to do this on any given house.....reduce spacing or increase mass. The only down side to having high mass in a radiant system is response time, but if the rest of the house is high mass, the temps don't need to fluctuate quickly. We have done a number of off grid houses with radiant stoves, high mass, and the temps rarely vary more than a few deg, even without supplemental heat.

I have seldom seen a reason for low mass radiant except for a builder who is not willing to wait for gypsum cement to dry out properly.


The response time is a huge issue in higher efficient buildings, which simply don't loose much heat, and usually have much solar gain.
High mass floors are taking hours to heat up and hours to cool down. They don't give you heat when you need it, and then still heat when you don't need it.
May be you can elaborate how a higher radiant mass will increase efficiency? What matters is the conduction from the pipe to the floor above. Yes, spacing is one way. Gypsum and concrete is a bad conductor, aluminum is much better.

Sure, aluminum is a better conduct but that is not a reason to use it, UNLESS, you have no other thermal mass in the house which is typical of most North American homes. I don't put t-stats in homes anymore except to switch over from heating to cooling (30% of the houses I work on have cooling). High mass systems work well with outdoor reset and good control strategies, anticipation of OD temp changes. The problem is that controls here are not built that way and in the land of high mass building (Europe) those controls are more commonplace.

I would have to go back to my old Wirsbo or Rehau manuals from 20 years ago, which show tube spacing and water temps for different construction methods ( I will search for them later) but for the same heat output, you need a higher water temp with gypsum or a 1.5" drypack than with a 4" slab or you need better tube spacing.  I can't give you a technical answer with the math as Dana probably could, but I have worked on 100s of houses over the years and have found it to be true. I understand that there is direct relationship between HX surface area and liquid or output temps, that is the easy part.
www.BossSolar.com
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
15 May 2012 02:05 PM
Posted By MikeSolar on 14 May 2012 08:42 PM
Dana1, here is a link to the IEA website on the development of the ASHP and GSHP. The report is a final one detailing best practices and in it you can find some system performance data. There are some ASHPs with COPs approaching 4 and GSHPs with COPs near5.

http://www.annex32.net/field_monitoring.htm

The difference, in my mind, between North American HPs and European units is partly one of holistic design. We tend to take heat distribution by forced air system as a given which they don't do. It is considered lowest common denominator in Europe and the floor heating or radiators is included in the building design from day one. Forced air would generally not be considered because it takes up space, is more noisy and uses more energy to move the heat than heating with water.

The people I know over there use, for example, tubing with a 4-6" spacing in concrete which can result in 30C EWT and a 5-7C dT. Very different practice from here.

The link to the full document download is here

Thank you for that!  Surveys are by nature lacking in detail, but it would be very interesting to know more detail on the "Average Best Practices" systems bar-graphed in figure 2, p12, eh?

Overall it still looks like the high-3s for the industry average on newer-better/best installations.  In figure 1 p.11 the center of the curve on the slightly older Swiss survey was still 3.5-ish, but with a few 1-sigma outliers in the >4 range.

To be sure low temp hydronic systems will (almost) always beat air-delivered heat on for whole-system COP (true for both GSHP & ASHP.)

Clicking on the markers for a particular "Best Practices" installation on the installed monitoring map then selecting "database" it'll open up a 1-pager that includes system info, including the SPF (average COP).  You'd have to look at other resources to figure out average weather and groundwater temps etc. for any given location, but there are still several "Best Practices" geo systems in northern Europe averaging under 3.  Most where a "design SPF heating" is specified have measured performance that misses the mark by 5-10%, eg:  http://www.sepemo.eu/hp-best-practi...[item]=795 but some are pretty close:  http://www.groundmed.eu/hp_best_pra...abase/411/

The description of the system design and low-temp radiant tubing layout & design for this one is a plausible explanation of what it takes to hit an average COP of 5.  I don't know of any US installations that are as carefully crafted or implemented.  The mean SPF of all systems in the SEPEMO best-practices database is still 3.8, not 4+.

So like with the ductless systems, I'm encouraged by where the state of the art can take you in well thought out, well executed systems, that report doesn't move my expectations much (if at all).  As with most complex heating systems, the quality and experience of the designer is the biggest risk/reward on achieving actual performance in GSHP, and the even amongst the best-practices monitored systems there are some (relatively) low performers- the bell-curve is wide.


MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
15 May 2012 07:41 PM
No problem. It just shows how much CAREFUL planning can make a difference but, to be fair, there are some low brow HPs in Europe too but because they are seldom designed for cooling, the heating performance can be optimized. Many manufacturers also include solar thermal right in the design, including the control, not just an add on. The Austrians seem to have the best equipment and the Swedes seem to have the lowest standard heat loss around.

When I am finished outsulating my double brick house, i will have the all the sensors in the walls for monitoring temps, solar production, ASHP run times and current draw. I want to emulate as much as possible the best European practice. I'm a big fan of thermal mass although it is hard to explain why it actually allows for lower liquid temps other than a pure surface area argument....get a thermal mass warm enough and it is another radiator. And, Entering water temps of 35C and LWT of 27C is hard to do in a floor without mass.

We seem to be stuck on stick framing and fibreglas, neither of which i like.
www.BossSolar.com
LbearUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2740
Avatar

--
16 May 2012 06:11 AM
Posted By Dana1 on 04 May 2012 12:04 PM
Directing the air flow at windows makes comfort & window-condensation sense for low performance windows with U values north of U0.34, but adds practically zero advantages with U0.25 & lower windows.

Adding a hard-coat low-E storm window over a U0.34-U0.6 double pane adds more comfort that siting the duct under a window, and is one of many efficiency upgrades that is usually more cost effective than extra geo tonnage to cover the heat loss difference for the lower performance building envelope.

With >=R20+walls and <=U0.25 windows even point-source heating works well, and it hardly matters where registers are located, leading to shorter duct runs.

Comfort is just one reason why I prefer highest-efficiency building envelopes over highest-efficiency heating systems.

But clearly, not being in the HVAC biz I have no idea what I'm talking about (ever!) :-)


Correct!

The old HVAC model of putting registers directly at windows was due to the fact that windows were valued with R-3 ratings or lower. They had horrid convection. Today, one can get windows that have R-Values of R-9 or higher. Add to that the triple pane design and these windows will have warm panes WITHOUT having a duct blowing at it. So the old HVAC model of blowing air at windows is no longer valid or needed.




joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
16 May 2012 08:07 AM
"Correct!

The old HVAC model of putting registers directly at windows was due to the fact that windows were valued with R-3 ratings or lower. They had horrid convection. ."

It wasn't bad windows in HVAC lore......Carbon monoxide deaths in the late 19th and early 20th century had people going to sleep and never waking up. People took to sleeping with the bedroom window open to mitigate the mysterious "night death". That is why old steam boiler systems have the radiators at the windows (and are grossly oversized).
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
16 May 2012 11:23 AM
Posted By joe.ami on 16 May 2012 08:07 AM
"Correct!

The old HVAC model of putting registers directly at windows was due to the fact that windows were valued with R-3 ratings or lower. They had horrid convection. ."

It wasn't bad windows in HVAC lore......Carbon monoxide deaths in the late 19th and early 20th century had people going to sleep and never waking up. People took to sleeping with the bedroom window open to mitigate the mysterious "night death". That is why old steam boiler systems have the radiators at the windows (and are grossly oversized).

Sounds like the perfect rationale for directing geo ducts at windows then, eh? There could always be refrigerant leaks, which could be disaster in a tight home unless you leave the windows open! 

Trade habits & conventions are hard to break, so the rationale for retaining them may shift:  In one era it's night-death, another it becomes window condensation. But at this point it doesn't take state-of-the-art windows to simply dispense with the heat-source-by-window design habit, especially when there are upfront cost and system efficiency reasons for doing so.
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
17 May 2012 10:00 PM
Windows are the source of most of our cooling loads, so I'll continue to aim cool air at them, although from well back in the room, circumstances permitting.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
18 May 2012 01:57 AM
Posted By docjenser on 14 May 2012 12:22 AM
Let me clarify this.==== to lower refrigerant pressured and higher COP. Thus radiant floors can be more efficient in heatpump applications than forced air.
Agreed IF and ONLY IF I am reading your head pressure gauges lower than the forced air refrigerant readings..., and a forced air that is high-efficiency distributed. Again, fire another thread.

Who has other curves or  tables of what was asked in the first question?

Nice comments by so many !

knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
18 May 2012 02:27 AM
T's Mike:

-Have to just be cutting to the chase  though.

1)
Put a compressor in between a 35 to 55% over sized air coil, and 55% oversized water coil as is the ratings mentioned, and there is the 4+ in AHP IF the energy exchanged Ex is that much greater at the over-old-standard 1:1 exchanger sizing.

Watch for the Climatemastering 40SEER, just like Hydro-Temp has IQ now... BIG Ex at having BIG HX coils....

Dana 'tis true, those putting 4 ton GT multi-multi stagers in and on 2.1/2- ton heating loads at ~ 15 to 20 above and with then 35- to 37 degre ground loops hitting 3+ gpm/the 4 tons is going to (without variable WILO pumps on the flow center, or grundfos ALPHA's on little ones, etc) get near COP 5's ONLY at the relatively leveraged mega dollar heat exchanger over-sizing. just in coldwater heating up the head pressures can be at (chilly) 85-88 degrees and suctions above 33-34 deg...  getting all that with a single 180-200 watt pump on the loop side. That is why I have metered under 8000 KWH for all HW and Heat and Cooling as well on 3500-3700 what I called 'typical' sub zero homes.
What is so interesting too is they had 80-100 dollar electric bills with propane or oil and now, with UNISULATED basements, still , have budgets under 130-134/month !!! Electric co other charges dropped with the higher kwh usage disproportionately.

2)
Mike: How many (high or low mass) steady-state Ex have you been able to see in , ugh- typical 6" wet-cellulose, wall, r-50 attic, under 35% glass northern homes are there really going to be 4+ AHP's in normal sub zero winters?  I am just asking nicely...

3)
Any 11-btuh to 11.3-btuh/sqft for comfortable 71-72 air temps? I have heard other testimony, but finding 11 btuh/sqft in more efficient HVAC forced air heating: Are there any you see way below that 11/sqft, in homes of  below zero weather, with open stairs to basement to rec area and large vaulted main floors above? About a few homes measured, but 'typical' for good air distribution and comfort is why I would like to compare to others data. (Having high return-air's)
MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
18 May 2012 06:41 AM
Posted By knotET on 18 May 2012 02:27 AM
T's Mike:

-Have to just be cutting to the chase  though.

1)
Put a compressor in between a 35 to 55% over sized air coil, and 55% oversized water coil as is the ratings mentioned, and there is the 4+ in AHP IF the energy exchanged Ex is that much greater at the over-old-standard 1:1 exchanger sizing.

Watch for the Climatemastering 40SEER, just like Hydro-Temp has IQ now... BIG Ex at having BIG HX coils....

Dana 'tis true, those putting 4 ton GT multi-multi stagers in and on 2.1/2- ton heating loads at ~ 15 to 20 above and with then 35- to 37 degre ground loops hitting 3+ gpm/the 4 tons is going to (without variable WILO pumps on the flow center, or grundfos ALPHA's on little ones, etc) get near COP 5's ONLY at the relatively leveraged mega dollar heat exchanger over-sizing. just in coldwater heating up the head pressures can be at (chilly) 85-88 degrees and suctions above 33-34 deg...  getting all that with a single 180-200 watt pump on the loop side. That is why I have metered under 8000 KWH for all HW and Heat and Cooling as well on 3500-3700 what I called 'typical' sub zero homes.
What is so interesting too is they had 80-100 dollar electric bills with propane or oil and now, with UNISULATED basements, still , have budgets under 130-134/month !!! Electric co other charges dropped with the higher kwh usage disproportionately.

2)
Mike: How many (high or low mass) steady-state Ex have you been able to see in , ugh- typical 6" wet-cellulose, wall, r-50 attic, under 35% glass northern homes are there really going to be 4+ AHP's in normal sub zero winters?  I am just asking nicely...

3)
Any 11-btuh to 11.3-btuh/sqft for comfortable 71-72 air temps? I have heard other testimony, but finding 11 btuh/sqft in more efficient HVAC forced air heating: Are there any you see way below that 11/sqft, in homes of  below zero weather, with open stairs to basement to rec area and large vaulted main floors above? About a few homes measured, but 'typical' for good air distribution and comfort is why I would like to compare to others data. (Having high return-air's)
The houses i have worked on have not used wet cellulose but just about everything else (tires, straw bale, old jeans, foams, etc) but it is not unusual to have sub 10btu/ft2 in some of the houses i have worked on as a heating/solar contractor. 35% glass is in the passive solar range and there have been quite a few of those but unfortunately I only get anecdotal evidence of actual heating costs in these houses but i can say, that with really low distribution temp needs, I doubt you will find many people happy to sit beside 78F air but for a lot of the year you can heat with less than 78F water if done right. 

I don't know of any ASHP that can produce a MEASURED COP of 4 at below freezing temps but I don't see why an ANNUAL 3.5 cannot be achieved with the right tube spacing and careful HP coil design AND I believe that with the solar/ASHP setup we are now designing, we will be able to get an annual COP of 5. I won't be able to report on that till this time next year, unfortunately. I am not holding my breath but if it comes in I will be quite happy. All this and the installed budget (solar included) will be about 65-70% of GSHP. That is the goal.

www.BossSolar.com
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
18 May 2012 07:58 AM
Zounds great the heating with 78 water.  Our basement rec slabs hold 71-73 with 75-78 respectively, but 5-6" first 4 runs from perimeter to 14-16" spaced in center low loads.

SOLAR boosted AHtP, as my cousine from Austrailia put it in 1981, were all for him government grant boosted and air to HW heating as well. He saw the pictures of the TETCO 1-ton w:w water heatersunder 40 gal amtrol tanks (inside DX of 4 (?30") columns of little ~2"dia.CuCoils run inside of that water vessel, a Dave Heart design of '79). Cous' is now an Engineer with directing some of the State of Victoria's Solar. Same year'81, an auto vocational teacher in Massilon near the Football Hall of fame (Canton) hybrid-looped in drain-down collectors on a ss tanker vessel -top 6- ft deep. Moist clay soil held temps down sow it was more effectual below 55 water (well water buffer, only). He believed 2) 3x6's delivered over 4500 btuh each on working on 45F waters.  

What do you think if you just raise the air temps through air solar collectors of high heat transfer, very low mass, low collector-heat-storage- capacity Air-Collector for some installed cost efficiency?  Boosting 1/3 at or in about 70% of a compressor (inside-labled) rating of 2 tons ::) then 18kB to ?20kB Ex cold-conditions might be such that we may corollate to solar air additions of near:

(ignoring constants)~  10F x 600 cfmuhmmm..! Then by a peanut Sol-Air-movement.
Seems that's under 1/6hp blowers similar to units re-capturing the heat off of gas-pool-water heaters power-vents (final stage HX pool water flowing heat-recovered) within those experimental add-on FanCoil, thin SS boxes.

200-300 watt blowers for a near 2 kw Solar Booster design of one collector in ? 10- to -10F air intake, getting over to AHP outdoor section ?
MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
18 May 2012 01:17 PM
Posted By knotET on 18 May 2012 07:58 AM
Zounds great the heating with 78 water.  Our basement rec slabs hold 71-73 with 75-78 respectively, but 5-6" first 4 runs from perimeter to 14-16" spaced in center low loads.

SOLAR boosted AHtP, as my cousine from Austrailia put it in 1981, were all for him government grant boosted and air to HW heating as well. He saw the pictures of the TETCO 1-ton w:w water heatersunder 40 gal amtrol tanks (inside DX of 4 (?30") columns of little ~2"dia.CuCoils run inside of that water vessel, a Dave Heart design of '79). Cous' is now an Engineer with directing some of the State of Victoria's Solar. Same year'81, an auto vocational teacher in Massilon near the Football Hall of fame (Canton) hybrid-looped in drain-down collectors on a ss tanker vessel -top 6- ft deep. Moist clay soil held temps down sow it was more effectual below 55 water (well water buffer, only). He believed 2) 3x6's delivered over 4500 btuh each on working on 45F waters.  

What do you think if you just raise the air temps through air solar collectors of high heat transfer, very low mass, low collector-heat-storage- capacity Air-Collector for some installed cost efficiency?  Boosting 1/3 at or in about 70% of a compressor (inside-labled) rating of 2 tons ::) then 18kB to ?20kB Ex cold-conditions might be such that we may corollate to solar air additions of near:

(ignoring constants)~  10F x 600 cfmuhmmm..! Then by a peanut Sol-Air-movement.
Seems that's under 1/6hp blowers similar to units re-capturing the heat off of gas-pool-water heaters power-vents (final stage HX pool water flowing heat-recovered) within those experimental add-on FanCoil, thin SS boxes.

200-300 watt blowers for a near 2 kw Solar Booster design of one collector in ? 10- to -10F air intake, getting over to AHP outdoor section ?

75-78 is not so hard in a basement with a slab but harder to do upstairs with more heat loss so the tube spacing has to be max 6"

The solar boost is not for the air side. Too much fluctuation and no storage. My system uses the solar thermal to up the evap temp.

I think it is better to have 3 low efficiency flat panels than 2 very high efficiency flat or tube panels. panels last longer, so does glycol

Not sure what this below means:

"Boosting 1/3 at or in about 70% of a compressor (inside-labled) rating of 2 tons ::) then 18kB to ?20kB Ex cold-conditions might be such that we may corollate to solar air additions of near:

(ignoring constants)~  10F x 600 cfmuhmmm..! Then by a peanut Sol-Air-movement.
Seems that's under 1/6hp blowers similar to units re-capturing the heat off of gas-pool-water heaters power-vents (final stage HX pool water flowing heat-recovered) within those experimental add-on FanCoil, thin SS boxes.

200-300 watt blowers for a near 2 kw Solar Booster design of one collector in ? 10- to -10F air intake, getting over to AHP outdoor section ? "
www.BossSolar.com
LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
18 May 2012 04:46 PM
Posted By MikeSolar on 18 May 2012 01:17 PM

Not sure what this below means: ..."Boosting 1/3 at or in about ..."

Maybe because you don't speak Klingon?

One measurement is worth a thousand expert opinions.
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
18 May 2012 05:11 PM
Posted By engineer on 17 May 2012 10:00 PM
Windows are the source of most of our cooling loads, so I'll continue to aim cool air at them, although from well back in the room, circumstances permitting.

The vast majority of the heat gain through windows is radiated, not conducted, even with low-E windows.

Radiated heat passes through cool air just as readily as through warm air-  the net effect of aiming the cool air at the window is negligible, whereas shading that window on the exterior has a huge effect.
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
18 May 2012 06:51 PM
isn't he just the cutest thing I wonder if he can read an answer questions at the beginning anyway .. thanks for your real effort mike and the rest what I was doing as I was estimating 1 third of the total load of absorbed heat outside ahp might need at the evaporator through the entire discussion as it was regarding solar boosting at the evaporator mode of the outdoor condensing unit a lot of people just called that condenser units section. it was merely a proposed guess to just see where they ending results would be about cfm . I wonder how many have experienced floor heating of the low mass upper level with less than 80 degrees that's great that you get something like that . Solar boosting has been discussed before I read in. 1980 Seems promising. I really wanted to pull out of the hat some things you may have come across mike so feel free to share with us as you seem to be in a 99 percentile sufficienttly enjoying this thread . I also believe blocks of ice are also part of referring to as the experienced as w.ell as a qualified technician to set things up . experience similar hardships in the humid winter weather belowlake erie. Mike--- I wonder more of what you mean by temperature differential and some other basis for your discussions about that as I read more of your responses I will understand your picture better . 'k-nough4now
LbearUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2740
Avatar

--
18 May 2012 08:45 PM
Posted By Dana1 on 18 May 2012 05:11 PM
Posted By engineer on 17 May 2012 10:00 PM
Windows are the source of most of our cooling loads, so I'll continue to aim cool air at them, although from well back in the room, circumstances permitting.

The vast majority of the heat gain through windows is radiated, not conducted, even with low-E windows.

Radiated heat passes through cool air just as readily as through warm air-  the net effect of aiming the cool air at the window is negligible, whereas shading that window on the exterior has a huge effect.

For a west facing window, what is the lowest SHGC that you would recommend for a window?


engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
18 May 2012 10:05 PM
The lowest you can get, consistent with tolerable visual light transmittance and budget. A load calc lets you model the effects of various values of SHGC. Spending more than a few extra bucks on a window with more favorable coefficients rarely pays back in a reasonable time.

Down here I push for SHGC in the 0.2x range for south and west glass unless there is excellent shade.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
LbearUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2740
Avatar

--
18 May 2012 11:06 PM
Posted By engineer on 18 May 2012 10:05 PM
The lowest you can get, consistent with tolerable visual light transmittance and budget. A load calc lets you model the effects of various values of SHGC. Spending more than a few extra bucks on a window with more favorable coefficients rarely pays back in a reasonable time.

Down here I push for SHGC in the 0.2x range for south and west glass unless there is excellent shade.

Where are you located at?

So even with the south facing windows, you want 0.2x on the SHGC level?

While it is considered a "mild" climate where I will build (Chino Valley/Prescott, AZ). I am going to go with 0.48 SHGC on the south windows to make use of the passive solar during winter.

I know anything below 0.40 for the VLT, it starts to seem like tinted glass.


MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
19 May 2012 09:04 AM
Posted By Looby on 18 May 2012 04:46 PM
Posted By MikeSolar on 18 May 2012 01:17 PM

Not sure what this below means: ..."Boosting 1/3 at or in about ..."

Maybe because you don't speak Klingon?


I tried klingon, nearly lost my vocal cords. Big fan of proper punctuation though.
www.BossSolar.com
MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
19 May 2012 09:16 AM
Posted By knotET on 18 May 2012 06:51 PM
isn't he just the cutest thing I wonder if he can read an answer questions at the beginning anyway .. thanks for your real effort mike and the rest what I was doing as I was estimating 1 third of the total load of absorbed heat outside ahp might need at the evaporator through the entire discussion as it was regarding solar boosting at the evaporator mode of the outdoor condensing unit a lot of people just called that condenser units section. it was merely a proposed guess to just see where they ending results would be about cfm . I wonder how many have experienced floor heating of the low mass upper level with less than 80 degrees that's great that you get something like that . Solar boosting has been discussed before I read in. 1980 Seems promising. I really wanted to pull out of the hat some things you may have come across mike so feel free to share with us as you seem to be in a 99 percentile sufficienttly enjoying this thread . I also believe blocks of ice are also part of referring to as the experienced as w.ell as a qualified technician to set things up . experience similar hardships in the humid winter weather belowlake erie. Mike--- I wonder more of what you mean by temperature differential and some other basis for your discussions about that as I read more of your responses I will understand your picture better . 'k-nough4now

I concentrate on heating over cooling, which is why I call it an evaporator. Just trying to be accurate. I don't have the numbers to say yet what the gains from solar heat injected into the evap will be but I suspect that as long as it is not snowing out, there can be some gain.

There is a large time frame, during lighted hours, when the panel temp is below that needed to heat DHW at all but it could boost the evap from, for example, -10C to 0C. This alone is a great improvement over the standard ASHP. The big issue is controls and this is where no existing package unit will work as they have a pretty rigid programming. You have to be capable of DDC controls to make it work to the best efficiency.

To top it off, Ontario has time of use electrical rates. Peak is around $12/kwh and off peak is $.07/kwh. At night when we cannot use the solar gain directly, we are heating at a reduced cost. Win/win in my estimation. 
www.BossSolar.com
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
20 May 2012 05:03 AM
Posted By MikeSolar on 18 May 2012 06:41 AM
Posted By knotET on 18 May 2012 02:27 AM
Watch for the Climatemastering 40SEER, just like Hydro-Temp has IQ now... BIG Ex at having BIG HX coils..../>


GSHPs usually don't have a SEER rating, I am sure you meant ERR in the 40s. It doesn't really come from the coil, it comes from the inverter driven compressor.
www.buffalogeothermalheating.com
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
20 May 2012 05:44 AM
Posted By Dana1 on 14 May 2012 11:29 AM
Posted By docjenser on 12 May 2012 01:15 AM
Posted By Dana1 on 10 May 2012 04:20 PM
I've not seen credible 3rd party data to support the notion that the average full system GSHP seasonal COP is in excess of 4 yet, despite the onesie-twosies at the 2 sigma margins.  But if you can show me where to find third party survey data on instrumented & monitored systems such as the dozens of mini-splits in the NW Ductless project I'd be very interested to look at it. The smaller-scale studies I've seen to date all point to mid-3s as the system average.


http://www.builditsolar.com/Projects/SpaceHeating/InField%20PerformanceTestingofGSHP_updated%2011_11_2010.pdf

You are right, good published studies are lacking, the one above is quite bad with very inefficient systems and lots of variances, which make me question the data. We see average total system COP in the mid 4s with 3 ton dual stage W-A, with an average heating season EWT of 38F. We have 15 Welserver online, and should summarize and publish the data.

I'd already seen that one, and it's consistent with several others. Question the data all you like, but until there's published evidence that the industry average has has moved forward from that point, I don't see any reason to believe that a typical GSHP installation are even close to averaging in the 4s yet.  In fact I haven't seen ANY third party tested system that beat 4 as a seasonal average, but I wouldn't necessarily be shocked to find an existence proof some day. Yet I tend to believe people who actually measure stuff when they have no financial interest in the outcome rather than blindly accepting vendors' spec sheets, or the marketing literature/protestations of installers.  Allegations aren't evidence.

Just as with mini-splits- the average in-situ performance of tested systems can hint at what's possible, but from the prospective buyer's point of view it's unwise to assume that you'll beat the industry average.  Best-case scenarios are rare, but of course better-studied better-designed implementations can industry averages.  Just as I wouldn't assume an average COP of 3 for a ductless in US climate zone 5 (even though I believe it's possible with an optimized oversizing factor), I can't assume an average COP of 4 for GSHP based on an installer's say-so or industry-insider lore.  \

Say whatever you like, but show me, and don't be too sensitive when others call THAT data into question.

As a crude measure of where to place expectations, in US climate zone 5, for now I put the backstop at 2.5 & 3.5 for ductless & geo respectively.  While it might be at the lower-efficiency side of dead-center on the bell curve, it's probably within a single standard deviation.  In US climate zone 4  that moves up to 3.0 and 3.5 based on the available evidence.   But the fact that average for one of the zone-4 sub-region in the BPA study was 3.4, the possibility that at least some installation in that mix was averaging about 4, seems likely while others were only 3. 

Of the two non-instrumented systems in climate zone 4 that I have first-person reported billing data on, an average north of 3 would be consistent with the power use.  A 4 average would be a bit surprising, but not entirely out of the question for one of them, but it hasn't been up for an entire heating season yet.

Note that the testers in the BPA study were unable to achieve the HSPFs published by Mitsubishi, either in the lab or in-situ, but were able to demonstrate that their lab measurements were consistent with the field-monitored performance.  But they COULD reproduce the Fujitsu-published HSPF both in the lab and in-situ.  But since Mitsubishi holds the lion's share of the installations in that study it's conceivable it skewed the averages downward slightly.  As the state of the art moves forward it should all be moving up incrementally.




The IEA data was a nice compilation of filed test out there in Europe. A few things came to my mind.
1) Many of the data was from installs 5-15 years ago, and monitored over a nice period of time. HP efficiency has significantly improved since then. 2) Pretty much everything on GSHPs was W-W. The systems performing with a lower COP were radiator heat, which requires higher supply temp. Understand the impact of the lift, and you can design more efficient systems. 3) A main reason for lower system COP is the parasitic loss of the loopfield circulation pumps, which were 10-35% in the commercial applications, and between 6-25% in the residential applications. In the typical W-A application here in the US, what is the difference between the AHRI COP rating and the actual field? The loopfield circulation power and the high torque for the fan. The loopfield can be designed differently with lower pressure drop, and you can get the pumping done with a high efficiency circulator consuming 100 watts. Plus add an amp for the higher blower torque. But that's is about it. So add an average EWT in the upper 30sF, (remember the COP is rated at 32F EWT for second stage), and you will see COP performance number in the mid 4s.
We only have real time COP displayed on some of our systems, I have to reprogram the WELs to display the average COP over the season, but will do so soon. The manufactures tables are actually very accurate and very reproducible. You are feeding a heatpump with a certain amount of flow and temperature, and it will perform in a very predictable way.
So why do you always have to imply financial bias as soon as someone disagrees with you. Just because someone works in the industry and therefore has a certain amount of expertise does not mean he is not doing everything he can to stay objective.
www.buffalogeothermalheating.com
MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
20 May 2012 07:42 AM
docjenser, what is the percentage of w/w vs w/a systems you put in? I put in the IEA report partly because Dana1 had not seen much evidence of higher COP systems but also to show the complexity of design out there. My point is that the W/A or A/A must run at a higher output temp for comfort reasons where W/W or A/W can modulate down to good radiant temps and the higher COP systems are typically W/W for that reason, which is why we don't see them as much here.
www.BossSolar.com
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
21 May 2012 12:32 PM
"So why do you always have to imply financial bias as soon as someone disagrees with you. Just because someone works in the industry and therefore has a certain amount of expertise does not mean he is not doing everything he can to stay objective."

It's not all about suspicions of financial incentive (though I acknowledge those factors exist).  HVAC installers and system designers do not generally use the same level of measurement standards of scientists & engineers, nor should they.  (But I'm sure your WELs all use NIST calibrated instrumentation that you keep updated with periodic testing, right?  )

And it has nothing to do with someone agrees with me or not, it's about backing assertions with evidence.  A forum poster's word isn't enough when the published evidence is all over the place, and doesn't support the case. The published evidence demonstrates to me that there's a design risk, and that optimistic assessments of actual efficiency are often not borne out in the real world implementation.  The real world pumping and air handler power would seem to be harder to nail down in practice than the performance of the HP itself.

It's not like I'm treating ASHP data any differently.  In the NEEA/BPA ductless test data the installations in the coldest locations (Eastern Idaho, the warm edge of zone 6/cold edge of zone 5) averaged a seasonal 2.84 for COP, but I'm wouldn't base expectations on the measured results of exactly 9 systems.  (Most of those were installed 5+ years ago too, shall we pooh-pooh it as lower-than reality, since the technology has since improved?)   It IS safe to say that any decent ductless should be able to average 2.5 or better in that climate though, even though I'm sure some installations in that climate will be operating well into the 3s.
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
22 May 2012 12:25 AM
Posted By Dana1 on 21 May 2012 12:32 PM
"So why do you always have to imply financial bias as soon as someone disagrees with you. Just because someone works in the industry and therefore has a certain amount of expertise does not mean he is not doing everything he can to stay objective."

It's not all about suspicions of financial incentive (though I acknowledge those factors exist).  HVAC installers and system designers do not generally use the same level of measurement standards of scientists & engineers, nor should they.  (But I'm sure your WELs all use NIST calibrated instrumentation that you keep updated with periodic testing, right?  )

And it has nothing to do with someone agrees with me or not, it's about backing assertions with evidence.  A forum poster's word isn't enough when the published evidence is all over the place, and doesn't support the case. The published evidence demonstrates to me that there's a design risk, and that optimistic assessments of actual efficiency are often not borne out in the real world implementation.  The real world pumping and air handler power would seem to be harder to nail down in practice than the performance of the HP itself.

It's not like I'm treating ASHP data any differently.  In the NEEA/BPA ductless test data the installations in the coldest locations (Eastern Idaho, the warm edge of zone 6/cold edge of zone 5) averaged a seasonal 2.84 for COP, but I'm wouldn't base expectations on the measured results of exactly 9 systems.  (Most of those were installed 5+ years ago too, shall we pooh-pooh it as lower-than reality, since the technology has since improved?)   It IS safe to say that any decent ductless should be able to average 2.5 or better in that climate though, even though I'm sure some installations in that climate will be operating well into the 3s.


I indeed make the effort to check the precision of the probes for the WELs prior to installing by hanging them all in a bucket of water, and they are surprisingly accurate, usually within 5/100 degree F. The biggest issue is then how the probes are mounted then, and I always calibrate them with a NIST calibrated needle thermometer, which gets it down to a 1/10 of a degree F. They are mounted with a heat transfer compound usually used for laptop processors (to conduct heat away). Given that we usually shoot for a 5 degree delta T, the margin of error is around 0.1F, or 5%. If I see a diversion from last years data by more than 5% I usually go out there and make sure the sensors are calibrated again.

http://www.builditsolar.com/Projects/SpaceHeating/InField%20PerformanceTestingofGSHP_updated%2011_11_2010.pdf

However, all the objective 3rd party studies do not standardize and control the installation standards. The above study is the best example. One system using 2 circulation pumps consuming 800 watts, even if only one heatpumps is running in first stage, adding up to 40% parasitic losses. In the other system they could not get the air out of the loop.
So far, I am missing any description in any studies about the efficiency of the system design. How good is than the best measurement standard if the systems measured are inefficiently designed?
www.buffalogeothermalheating.com
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
22 May 2012 12:04 PM
"So far, I am missing any description in any studies about the efficiency of the system design. How good is than the best measurement standard if the systems measured are inefficiently designed?"

I share your frustration, but this is exactly the design-risk problem I refer to (often), and why I don't have faith that the industry average efficiency of GSHP has hit the 4s yet, and even though it's possible (or maybe even likely) that YOUR averages may beat that average by good measure.  Designing a maximally efficient system is not a trivial task.

With ductless ASHP the design risk is low since it's a "system in a can", even though sizing relative to the actual load has an effect efficiency.  But in cold climates it's going to be significantly less efficient than GSHP, most of the time.

In the 2010 paper you linked to, the full system wintertime average peformances of the three systems monitored were in the mid-3s, and at least in the CT & VA systems a better-class ductless would match or even beat them on seasonal performance at about 1/3 the upfront cost.  (I'd be pretty disappointed to have paid $40K for a system that performs no better than a $12K multi-split, as the VA client did.)  In the VA system, even though it's a large house, I question whether they really needed 6 tons to heat & cool the place too.  I suspect they could have stripped a lot in cooling load with better-optimized glazing & window placement, and the wall-R only meets the current code-minimum.  It feels like a case of designing the house off a prescriptive list rather than energy-use modeling, and without optimizing for value on non-so-cheap mechanicals against a higher-performance building envelope. But just as the system details are lacking, the envelope descriptions are also pretty sketchy.

Clearly system designers need to do a better job of maximizing the efficiency potential of GSHP.  Sure, it's just three systems, but it's consistent with the other drips & drabs of 3rd party tested systems out there (albeit dated evidence, in some cases.)  Should we be setting expectations based on three systems?  Maybe not, but in the absence of better evidence it becomes the "...you should be able to achieve at least..." benchmark.  Presuming those to be statistical outliers would be wrong in the absence of evidence to support that thesis.  Safer to assume you'd be able hit ~3.5, before plunking down the $30-40K (as those customers did), than building your financial analysis on an assumption of hitting 4.0,  just as it's safer to assume with ductless that you'd hit a COP of at least 2.5 in a US zone 5 climate based on the entirety of the available evidence, even though it's been demonstrated that 2.8+ is possible even on the cold edge of zone 5.
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
22 May 2012 11:32 PM
Posted By MikeSolar on 20 May 2012 07:42 AM
docjenser, what is the percentage of w/w vs w/a systems you put in? I put in the IEA report partly because Dana1 had not seen much evidence of higher COP systems but also to show the complexity of design out there. My point is that the W/A or A/A must run at a higher output temp for comfort reasons where W/W or A/W can modulate down to good radiant temps and the higher COP systems are typically W/W for that reason, which is why we don't see them as much here.


I agree. About 70% are w-a, the rest w-w. I try to design new w-w system for 85 degree supply temp for that reason. Not possible with water to air.
www.buffalogeothermalheating.com
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
23 May 2012 12:27 AM
Posted By Dana1 on 22 May 2012 12:04 PM
...this is exactly the design-risk problem I refer to (often), and why I don't have faith that the industry average efficiency of GSHP has hit the 4s yet, and even though it's possible (or maybe even likely) that YOUR averages may beat that average by good measure.  Designing a maximally efficient system is not a trivial task.

With ductless ASHP the design risk is low since it's a "system in a can", even though sizing relative to the actual load has an effect efficiency.  But in cold climates it's going to be significantly less efficient than GSHP, most of the time.



You certainly make a good point that the risk is lower with a mini split, since their system design is very much standardized. And that the risk is higher with a geosystem. But the point is, what everyone here is stressing, that there are good guys out here, who build and design efficient systems and that a good installer should be a first criterion, so you don't put your mid 20K (I don't know where the $30-40K average comes from) at risk.

I still don't see how you can weight a whole house system with a ductless. Both have their places, but they are different, as discussed to the exhaust here.

You can pretty consistently hit mid 4s with W-A, but that is it unless you are dealing with higher EWTs. W-W you can easily get above a COP of 5. I'll post it here soon and hope you find the methods legit. The reason I cited that paper is because it was a perfect example for inefficient system design.
www.buffalogeothermalheating.com
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
23 May 2012 10:04 AM
Posted By docjenser on 23 May 2012 12:27 AM
 
so you don't put your mid 20K (I don't know where the $30-40K average comes from) at risk.


Yes Dana,
You are fairly even handed, but doc and I have quoted mid 20's to less than 20k (respectively) for heat pumps installed turn-key, yet you keep insisting that systems are much more expensive.

Perhaps they are in some location, but as we speak from our own experiences, I cost compare to about 18K for a 3 ton. ASHPs get a lot less attractive with that in mind.

If it were 40K for a 3 ton around here, I probably would push air source.
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
23 May 2012 11:59 AM
Posted By docjenser on 23 May 2012 12:27 AM
...You can pretty consistently hit mid 4s with W-A, but that is it unless you are dealing with higher EWTs.

I agree. In my case, I consistently hit near 5.0 COP whenever I measure it. Indeed, I never see EWTs lower than 60 degrees F. Thank you for providing the article. I read it with interest. I believe that COP needs to be measured statistically, and not per the article's methodology. In the histogram below, it shows every COP measurement for every 1 minute, for an entire month, with no need to make judgement on which data points are good and which ones are not. This is actual data for my WF Envision GSHP. Best regards, Bill
Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
23 May 2012 12:31 PM
The $30-40K wasn't an average, it was the reported system costs to "...those customers..." as documented in the paper docjenser referred to.

http://www.builditsolar.com/Projects/SpaceHeating/InField%20PerformanceTestingofGSHP_updated%2011_11_2010.pdf

If you're gonna post it, why not actually read it, eh? :-)

The $40K system was 6 tons, not 3, which at $6.7K/ton would be a bargain at local rates for GSHP.. In MA installed costs for recent systems on geo averages just shy of $9K/ton, according to reliable MA state sources, which would put a typical 3-tons in the $25K-30K range. That is consistent with my (less-thorough and non-compiled) sample set. I've never seen or heard of a local quote for 3 tons of geo that came in under $20K, but again, it's a small sample- that may happen. Until there's data indicating otherwise I'll use the MA-state $9K/ton figure for generic estimation purposes rather than Joe's $6k/ton, unless that $18K for a 3-ton system the cost after the 30% tax credit subsidy(?).

I'm thrilled to know that there are good guys out there who can deliver designs that consistently hit the mid-4s, but it would be more comforting if third party investigators going out to measure performance on (presumably) randomly selected systems were coming up with averages better than mid-3s. It would be stupid to presume that they just randomly hit the bottom-of-the-barrel system designs, and that those designs not representative of where the industry average is.

This is comparable to the differences between "best-possible" and industry-average on the in-situ performance of retrofit condensing gas boilers- sure, a good designer can get 95%+ out of them, but in the average system they're struggling to beat 86%, despite equipment that scores in the mid-90s on an AFUE test. And of course better designers (or even alert amateurs) can point to why those underperforming systems don't hit the mark, but that doesn't affect the reality of where the industry average lies. The average customer may still be happy with the 86%, given that the typically oversized high-mass beast that was replaced was likely running in the 70% range. I suspect the typical GSHP buyer isn't an energy nerd sniffing hard at the true performance, but is rather just thrilled at how much less it costs to run than propane or oil.

Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
23 May 2012 12:47 PM
Posted By Dana1 on 23 May 2012 12:31 PM
... In my installed costs for recent systems on geo averages just shy of $9K/ton, according to reliable MA state sources, ...


C'mon, how does any geo professional get any residential customers at $9K/ton? For conventional W-A, closed loop, with a bore hole field? Nothing but granite to trench/drill through, requiring Interstate Highway construction size equipment to trench/bore the loop field, with an army of 100 workers? At what point does the cost of heating oil or electricity have to get to where the residential customer can see even a 10 year break even point? Best regards, Bill
Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
23 May 2012 03:18 PM
Posted By a0128958 on 23 May 2012 12:47 PM
Posted By Dana1 on 23 May 2012 12:31 PM
... In my installed costs for recent systems on geo averages just shy of $9K/ton, according to reliable MA state sources, ...


C'mon, how does any geo professional get any residential customers at $9K/ton? For conventional W-A, closed loop, with a bore hole field? Nothing but granite to trench/drill through, requiring Interstate Highway construction size equipment to trench/bore the loop field, with an army of 100 workers? At what point does the cost of heating oil or electricity have to get to where the residential customer can see even a 10 year break even point? Best regards, Bill

How, you ask?

Massive subsidy (both state and federal), and sky-high regional propane and oil pricing, pure and simple.  It's likely that the average $/ton will drop if the subsidies go away, or if the competition in the local industry picks up.  But I'm not just making this up, if that's what you're thinking- the roughly $9K/ton number comes from multiple sources.

I'll try to dig up the MA state cost data and post the link- it's available on-line, but buried in a larger energy policy document, not a 3 pager. IIRC the approximate average for GSHP systems was cited at $8.8K/ton for closed-loop, ductless air source $2.7K/ton, both of which are consistent with recent experience.  Other documentation I've seen (which may or may not be online) indicates that in neighboring CT systems that qualified for rebate under a state sponsor GSHP subsidy averages about $9K/ton for residential systems. 

A forward-looking analysis developed for the MA D.O.E. projects that future costs for GSHP systems will be $7.5K/ton (see section 7.4.1, p.95, p. 104, pdf pagination ) after further market development, and base their financial projections on a $7.5K/ton number.  But that number is speculative based on a number of factors, not existing-reality documented average, whereas the recent CT rebate program figures are based on hard data. (That paper also cites the $9K/ton number from the CT state program, albeit without referencing a hard documentation source.)

If you can beat that price with ease, maybe you could get rich by moving here. (PLEASE move here, I'd LOVE to see the cost drop to $6K/ton, if you really think that is realistic!)  But the available data points to $9K/ton is what it costs here, now, today.  Like the range of real-world average COPs the range in system costs is large, but to date I've yet to see or hear of any geo system (any size) installed in my neighborhood for under $20K.  Maybe they exist (just like systems with actual seasonal COP of 5+),  but they must be as rare as Catamounts- while everybody has heard the rumors, almost nobody claims first-hand experience. YMMV.

Electricity prices average ~15cents/kwh in this state, but there is a wide variance among the municipal utilities and between them and the larger regional operators.  Subsidized geo is an easy argument for most, but is still viable without subsidy on a longer time frame when the competition is $3 propane or $4 oil.  I've seen multiple instances this year of houses with heat loads under 3 tons that paid over $4K for heating fuel this season, and this was one of the mildest winters on record.  But for those people the payoff is 5 years or less (if not as deep as GSHP in a 20 year analysis) by retrofitting ductless ASHP to handle a large fraction of the heating load, even assuming a COP of 2.5.  It gets even shorter if one pushes the envelope and uses an average of 3.0, a performance I believe to be possible for ductless in this climate, but would not assume it to be typical.
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
23 May 2012 05:30 PM
seems to me any GT oversized exchangers for low 1st staging load comparison can come up with 5cop. And now 1.4 t at compresor IQgshp ver rfg. Low stg. in a size 4.1/2 "ton" typically is found today with near 6 ton air and water coils getting easy high's then. BUT D1's annual cyclic eff near 4 is so very design/er specific for 55 to 50 earth loops as he pointed out
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
23 May 2012 06:28 PM
Dana, thanks!

Wow! What a different market than what exists here in the Dallas area. For us, heating is an after thought, and NG is common to have for heating. Size the HVAC equipment (whatever it is) for cooling, and you don't have to worry if you've got enough heating capacity.

Versus (from the report you cited - thank you by the way):

"... only 29% of households in MA currently employ central air conditioning."

"... and for those that have it, most residences report using air conditioning on a limited basis - usually at night."

"... and further for those that have it, over 50% say they use air conditioning 2 of fewer days during the week in the cooling season."

The report goes on to say, for using GSHP in MA, at the estimated $8.8K/ton cost:

"5.3 years simple pay back if replacing electricity space heating."

"9.2 years simple pay back if replacing fuel oil space heating."

"41 years simple pay back if replacing NG space heating."

So it looks like the market average price per ton for GSHP in MA is in line with the pay back. Here in TX, where all of the dynamics are different, still, it's the same on simple pay back, at 5 - 10 years.

So if I read the report correctly, GSHP installation professionals, for residential, should be in MA, not TX, to maximize their gross revenue at $9K/ton, because it is definitely *not* nearly that high in TX!

But, at least here in TX it's not so difficult: casually walk through the home and tell the customer it's easy simply using the same amount of tonnage as currently exists (no need for a Manual J), contract with a drilling company for a standard one 300 ft borehole per ton drilling into sandy loam clay soil, slap in a GSHP unit up in the hot, unconditioned attic where everyone else's A/C air handler and furnace is, connect up the water pipes and purge, reconnect the supply and return main ducts, and you're done! Don't even have to have a refrigeration license because the most harmful medium you'll mess with is water (don't even need antifreeze)! (Never mind the professional, technical and geological expertise needed to make it all work well.)

Thanks,

Bill
Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
23 May 2012 07:28 PM
PA OH WV KY TM IA MI
Hello MA:

About states where there are several who could ---

Deliver GT systems with 4 zones control and 6 dampers dual compressors 3 staging plus supplemental, and
priority hot water heat recovery 100% while cooling, and On-Demand
and at least 1 ton oversized coils , 4 stats; and ON SITE startup in MA, gladly, near any 4.1/2 "size" GTHP
...@
Well under....14k. BEFORE CREDITS.... WITH DHW 1/6hp bronze and
Flowcenter and kit to unit.... infra red palm 8 sensor logging, etc.
Plus loop or well connected and setting in place and distribution duct, etc
ChrisJUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:277

--
24 May 2012 09:17 AM
KnotET

"Deliver GT systems with 4 zones control and 6 dampers dual compressors 3 staging plus supplemental, and
priority hot water heat recovery 100% while cooling, and On-Demand
and at least 1 ton oversized coils , 4 stats; and ON SITE startup in MA, gladly, near any 4.1/2 "size" GTHP
...@
Well under....14k. BEFORE CREDITS.... WITH DHW 1/6hp bronze and
Flowcenter and kit to unit.... infra red palm 8 sensor logging, etc.
Plus loop or well connected and setting in place and distribution duct, etc"

Well under...14k,?? then my Hydro-temp dealer made a killing on me!!! And a piss poor warranty to boot!!

If I had learned more about GSHP systems before I purchased, I don't think I would have gone with Hydro-Temp. They got me hook, line and sinker, system does everything I want, radiant in basement, air on main floor and 100% DHW. It is very cheap to operate, but I am scared to death of repair bills in 4-5 years!

ChrisJ
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
24 May 2012 09:34 AM
Posted By Dana1 on 23 May 2012 12:31 PM
The $30-40K wasn't an average, it was the reported system costs to "...those customers..." as documented in the paper docjenser referred to.

http://www.builditsolar.com/Projects/SpaceHeating/InField%20PerformanceTestingofGSHP_updated%2011_11_2010.pdf

If you're gonna post it, why not actually read it, eh? :-)

The $40K system was 6 tons, not 3, which at $6.7K/ton would be a bargain at local rates for GSHP.. In MA installed costs for recent systems on geo averages just shy of $9K/ton, according to reliable MA state sources, which would put a typical 3-tons in the $25K-30K range. That is consistent with my (less-thorough and non-compiled) sample set. I've never seen or heard of a local quote for 3 tons of geo that came in under $20K, but again, it's a small sample- that may happen. Until there's data indicating otherwise I'll use the MA-state $9K/ton figure for generic estimation purposes rather than Joe's $6k/ton, unless that $18K for a 3-ton system the cost after the 30% tax credit subsidy(?).

I'm thrilled to know that there are good guys out there who can deliver designs that consistently hit the mid-4s, but it would be more comforting if third party investigators going out to measure performance on (presumably) randomly selected systems were coming up with averages better than mid-3s. It would be stupid to presume that they just randomly hit the bottom-of-the-barrel system designs, and that those designs not representative of where the industry average is.





The cited study is the "bottom of the barrel" design. Grossly oversized loops (nice EWT though), multiple inefficient circulation pumps, inability to purge air out of a loop. I would be embarrassed! No word on how the instruments were calibrated and the numbers were measured. But the fact that 3rd party investigators did it makes this study now creditable and valid as a norm?

www.buffalogeothermalheating.com
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
24 May 2012 09:35 AM
Further thinking about GSHP installations in MA:

It looks to me that, in the case of a home having a NG supply, and already having a forced air duct system, noting that there's little need for cooling, it would be a no brainer in favor of putting in classic, NG forced air furnaces, versus GSHP.

Best regards,

Bill
Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
24 May 2012 03:36 PM
Posted By a0128958 on 24 May 2012 09:35 AM
Further thinking about GSHP installations in MA:

It looks to me that, in the case of a home having a NG supply, and already having a forced air duct system, noting that there's little need for cooling, it would be a no brainer in favor of putting in classic, NG forced air furnaces, versus GSHP.

Best regards,

Bill

Most gas fired heating in MA is hydronic, either steam radiators or pumped hot water baseboards (sometimes radiators, or radiant floors), but 2-stage condensing gas is starting to become common in code-min tract homes where they want ducted air-conditioning as well.  Most MA homes where AC has been retrofitted are still heated with hydronic systems.

All mid-sized cities in MA are on the gas grid, but not all streets in those cities are on gas mains. There are still a lot of homes off the gas grid in the less dense areas, where traditionally heating oil has been the predominant fuel of choice, but with a sizable number of propane-burners too, as well as (believe it or not, even at 15-22cent/kwh) electric baseboard & electric radiant heated homes.

Retrofitting THESE homes are what is going to drive the heat pump market here, but in the 'merican tradition of never looking past 3 years for payback on any home improvement (18months is long for most), GSHP is still a hard sell even with subsidy.  But now that (relatively) cheap ductless has improved to the point that it can deliver significant heat southern New England design temps and is pretty much guaranteed to deliver seasonal COPs well north of 2, and can even bump on 3, the payback on them is pretty quick, and should be an easier sell to those with short horizons.  In CT there's a $1000 rebate for mini-splits, and a $1200 ton rebate for GSHP.

The only people I know personally in MA who have installed GSHP are A: Living in their dream-homes for the long term B: VERY well-off financially (the 2%, if not all 1%-ers ) and C: Very environmentally conscious, willing to spend more for the higher efficiency, up to a point.  The hard-corps middle-class greenies in MA spend it on the building and heat with mini-splits, living in more modestly sized, modestly appointed but quite immodestly-insulated houses, and if there's a trend, it seems to be more toward the PassiveHouse/Net-Zero end than toward bigger-better-nicer houses with highest-possible efficiency mechanical systems.  But if GSHP were running $6K/ton and regularly hit the 4+ COP potential, there would be more interest from the local green crowd.

In CT there's a $1000 rebate for mini-splits, and a $1200/ton rebate for GSHP, but note the average  system size is 4.77 tons, and average system cost is over $40K, given the average cost/ton of $8,782.00 (see the table in the middle of that page.)   Ratepayer & taxpayer money going into the pockets of the very well off, mayhaps?  Rebates for high-efficiency ductless ASHP is a more modest $1000-max and then only for homes/zones hard-wired with electric resistance heating.  From a policy point of view there's more lifecycle carbon being offset per rate/tax-payer subsidy dollar with the ductless rebate program, a technology that is not being incentivized by Uncle Sugar the way GSHP systems are.  OTOH the reduction in wintertime peak grid loading isn't as good with the ASHP either, since at CT-style design temps the COP is only in the low 2s, so it depends on what the total mix of policy goals are.

Note that the lifecycle cost analysis and other financial comparisons in that MA analysis paper use $7.5K/ton for GSHP costing, despite having mentioned the current actual $8.8K average cost.  At current real-world costs the simple payback periods are longer, the IRR smaller, NPV lower, since the upfront cost is 17% higher than in the analyses.
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
24 May 2012 04:02 PM
docjenser: I hear you on both the quality of the design and qualifications of those who did the measurement, but it's the study YOU pointed to- should I assume it's YOU doing some cherry-picking, only putting up bottom of the barrel designs for discussion? ;-)

But seriously, I don't know how all third party testers manage to randomly select bottom-of-barrel designs if that doesn't in some way represent the industry average. The more publications there are out there like that, the narrower the 1-sigma error bars become. Until I see something different I'm not going to assume the industry average is dramatically better. Just because a good designer COULD do better means squat, if every time somebody throws a dart at the sample it lands on crap. We need more numbers to find the true 1-sigma limits, but every documented independently measured US installation I've found online comes up in the 3s, sometimes the low 3s, sometimes the high 3s, but I've still not seen 4. And most of these appear to be put up as examples of just how green these houses & systems are, yet it's easy to find fault with both the building envelope and the mechanical designs with only a small amount of analysis.

And that guy in VA who dropped $40K+ on 6 tons of geo should ask for his money back if they won't or can't fix the design errors and get his performance at least above 3.5. At VA winter temps & dew points a ductless would hit his 3.3-3.4 average pretty easily.
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
24 May 2012 04:09 PM
Dana, thanks. Best regards, Bill
Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
24 May 2012 04:35 PM
Posted By a0128958 on 24 May 2012 04:09 PM
Dana, thanks. Best regards, Bill

Yer welcome!

Does this mean you're going to pull up stakes & come north to bring the local price average for GSHP down to something under $8K/ton, and get rich in the process?   (Bring some winter clothes if you do.)
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
24 May 2012 05:01 PM
Nope! If you do it right, there's plenty of opportunity here! It's really no different than anywhere else - to get geo working right requires a lot of water loop expertise and geology knowledge.

It's just a different set of challenges down here. Imagine, for example, having to worry about wearing out your borehole field! I've got a friend down the street, whose EWT now goes North of 105 degrees every Summer. Each year EWT has gotten a little higher, as the Earth has not ever had enough time to absorb all of the heat being put into it. Course of time is about 15 years.

Best regards,

Bill
Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
24 May 2012 07:33 PM
105F ... Each year EWT has gotten a little higher,


That's when you wish you had some groundwater flow to carry that heat off to your neighbor :-)
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
24 May 2012 11:35 PM
In a cooling-dominated climate an EWT anywhere near or above ambient air temperatures begs the question of why spend $15k on a complicated system of bores, pipe and pumps when the $200 fan motor and blade on a conventional ASHP gets to reject heat into same or cooler heat sink?

I suspect that for geo to be successful in cooling dominated climate EWT must be consistently 5-10*F below design outdoor air temperature. Otherwise EER and COP fall to the point that conventional split or minisplit ASHP make more sense.

An obvious exception (that buys some of my steak and beer) is beachfront homes whose blown sand and salt air dramatically shorten life of ASHP outdoor units.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
25 May 2012 12:27 AM
Posted By engineer on 24 May 2012 11:35 PM
In a cooling-dominated climate an EWT anywhere near or above ambient air temperatures begs the question of why spend $15k on a complicated system of bores, pipe and pumps when the $200 fan motor and blade on a conventional ASHP gets to reject heat into same or cooler heat sink?

I suspect that for geo to be successful in cooling dominated climate EWT must be consistently 5-10*F below design outdoor air temperature. Otherwise EER and COP fall to the point that conventional split or minisplit ASHP make more sense.

An obvious exception (that buys some of my steak and beer) is beachfront homes whose blown sand and salt air dramatically shorten life of ASHP outdoor units.

My friend gave up last year, and instead of 'refurbishing' his borehole field, he cut the pipes and had ASHPs put it.  With some of the boreholes within 10' of each other, with the prospect of re-drilling these, at $1K each for 300' depth, and with the strong probabiliy of adding more boreholes, again at $1K each, along with reconnecting up the loop pipe, the cost was just too much compared to simply saying 'goodbye' to the borehole field and putting in ASHP units.

The heat here is an absolute killer.  And, the ASHP guys easily can come in, in one afternoon, and have you all fixed up.  Actually, the 'Christmas season' has already started for the ASHP guys.

I feel lucky.  My EWT doesn't yet get above 85°, no matter how hot it gets.  But I'm watching it over the next few years.

I don't know what design outdoor air temperature is for Dallas.  I do know record temperature is about 112° F. 

P.S., my visitors last year for the home energy tour asked why my grass was still green in my front yard, where I have 8 wells with a total of about 1 mile of pipe.

Best regards,

Bill
Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
MikeSolarUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:376

--
25 May 2012 06:33 AM
Posted By a0128958 on 25 May 2012 12:27 AM
Posted By engineer on 24 May 2012 11:35 PM
In a cooling-dominated climate an EWT anywhere near or above ambient air temperatures begs the question of why spend $15k on a complicated system of bores, pipe and pumps when the $200 fan motor and blade on a conventional ASHP gets to reject heat into same or cooler heat sink?

I suspect that for geo to be successful in cooling dominated climate EWT must be consistently 5-10*F below design outdoor air temperature. Otherwise EER and COP fall to the point that conventional split or minisplit ASHP make more sense.

An obvious exception (that buys some of my steak and beer) is beachfront homes whose blown sand and salt air dramatically shorten life of ASHP outdoor units.

My friend gave up last year, and instead of 'refurbishing' his borehole field, he cut the pipes and had ASHPs put it.  With some of the boreholes within 10' of each other, with the prospect of re-drilling these, at $1K each for 300' depth, and with the strong probabiliy of adding more boreholes, again at $1K each, along with reconnecting up the loop pipe, the cost was just too much compared to simply saying 'goodbye' to the borehole field and putting in ASHP units.

The heat here is an absolute killer.  And, the ASHP guys easily can come in, in one afternoon, and have you all fixed up.  Actually, the 'Christmas season' has already started for the ASHP guys.

I feel lucky.  My EWT doesn't yet get above 85°, no matter how hot it gets.  But I'm watching it over the next few years.

I don't know what design outdoor air temperature is for Dallas.  I do know record temperature is about 112° F. 

P.S., my visitors last year for the home energy tour asked why my grass was still green in my front yard, where I have 8 wells with a total of about 1 mile of pipe.

Best regards,

Bill
$1000/hole!!!!! The going retail rate up here is $2500-3000. I don't know how you make a living at that rate. Anyway, the ambient temp argument is one of the the reasons I concentrate on ASHPs and i think that is the future.

www.BossSolar.com
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
25 May 2012 12:33 PM
Posted By a0128958 on 25 May 2012 12:27 AM
Posted By engineer on 24 May 2012 11:35 PM
In a cooling-dominated climate an EWT anywhere near or above ambient air temperatures begs the question of why spend $15k on a complicated system of bores, pipe and pumps when the $200 fan motor and blade on a conventional ASHP gets to reject heat into same or cooler heat sink?

I suspect that for geo to be successful in cooling dominated climate EWT must be consistently 5-10*F below design outdoor air temperature. Otherwise EER and COP fall to the point that conventional split or minisplit ASHP make more sense.

An obvious exception (that buys some of my steak and beer) is beachfront homes whose blown sand and salt air dramatically shorten life of ASHP outdoor units.

My friend gave up last year, and instead of 'refurbishing' his borehole field, he cut the pipes and had ASHPs put it.  With some of the boreholes within 10' of each other, with the prospect of re-drilling these, at $1K each for 300' depth, and with the strong probabiliy of adding more boreholes, again at $1K each, along with reconnecting up the loop pipe, the cost was just too much compared to simply saying 'goodbye' to the borehole field and putting in ASHP units.

The heat here is an absolute killer.  And, the ASHP guys easily can come in, in one afternoon, and have you all fixed up.  Actually, the 'Christmas season' has already started for the ASHP guys.

I feel lucky.  My EWT doesn't yet get above 85°, no matter how hot it gets.  But I'm watching it over the next few years.

I don't know what design outdoor air temperature is for Dallas.  I do know record temperature is about 112° F. 

P.S., my visitors last year for the home energy tour asked why my grass was still green in my front yard, where I have 8 wells with a total of about 1 mile of pipe.

Best regards,

Bill
 The 1% number for Dallas is 98F, so I think you have a ways to go before it underperforms conventional 1 & 2 stage ducted air source AC.
chrisbikerUser is Offline
New Member
New Member
Send Private Message
Posts:97

--
25 May 2012 01:49 PM
Just for your yardstick reference. East Pa area. I had 4 bids for geo for my house 2 years ago. Replace existing 4T ASHP with 2 stage 4T geo W-A, borefield, DSH, use existing ducts. Bids came in from 22 - 30K. I ended up at $23K with 3x260' bores. EWT stays above 40F all winter.

So thats $5.75K/Ton.

System is fantastic so far. House is more comfortable and electric use is waaayyyy down. We run it more that ASHP, since its so economical to run . I calc'ed payback at 8 years vs high end ASHP after rebates at our electric rates.

Never considered mini's. Not really suitalbe for our 2 story colonial. No central circ, filter, or humidification in winter. Existing ducts already there. etc...

Chris
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
25 May 2012 01:56 PM
Posted By Dana1 on 25 May 2012 12:33 PM
l
 The 1% number for Dallas is 98F, so I think you have a ways to go before it underperforms conventional 1 & 2 stage ducted air source AC.

Dana, thank!  Best regards,  Bill
Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
25 May 2012 01:58 PM
At some point, the quest for higher COP is better achieved with air source to hydronic storage running at night (when it is ~20F cooler). 10 foot borehole spacing wasn't a good idea.
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
25 May 2012 04:28 PM
Chris- Clearly that would be a super-bargain, in my neighborhood! (Even your high-bid of $30K for 4-tons would beat the local average here by about five grand, but it's likely that SOME 4T system here would hit that number.)

You probably took the 30% tax credit, bringing the out-of-pocket to about $16K before other state & local subsidies? What was the final post-subsidy cost?
robinncUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:586

--
25 May 2012 10:14 PM
Dana......to get the price down to 6K/ton up there.....get ride of the unions     :)
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
26 May 2012 07:23 AM
Fantastic C:  !!!
In Harrisburg PA
with a 5-ton dual compressor [3-staging, 18MBtu first] w/ 100% Domestic-HW (in cooling mode 100%, loop pumps shut off) - - - $Top of the line$- I think you will find a very happy psychologist, who sends me Harry and David's fruit each year, spent less than that $5.7/'ton';and with a new duct system (less labor, he put in ducts) [eh? compares to mini's?] !
That is in part w/ 3x240' bores and (not always recommended, oly twice installed since 1983 !) all in/on ONE single 1.25 line x ~ 1,600ft, saved more installed costs @ no headers nor labor-intensive building etc., comparatively. His driller even horizontally drilled, 'moled' 12+ feet into basement wall, saving other costs. Loop stays above 35, and the 5-(real compressors inside unit) tons are like "Size 5.8-6.0's" in among other brands 'ratings', and that would put it even far less than even $5.2k/t.

His in-floor radiant slab-walkout- 1/2-finished-basement +all 2 top floors, has- alone- over a 30-yr ROI, compared to since he can comfortably heat, very inexpensively, with just using the (better-directed) forced-air. Air in this GT- is always at- 3 or 4F above any 'tepid' misconcerns. The system has 96F-97F air temp set with modulating blower speed controlled by a changeable program set point (living 67-deg, is made more comfortable). Claims all utilities in  about 3200 living w/ 1200 basement only insulated from 2ft below grade to exposed walls R-6, to R-7, but foiled-foam boards: @ $ 93.-$95 per mo, budget, family of 2. His prog.set.back.thermostat is used a lot  b/c of w/ an oversized and staging GT (Strip KW supplement is turned off for the past 4 years to  -5F's). That same size/type GT System is heating 4400 sq ft to a  -10F below, different insulation over 1800 basement sq ft. w/ not using supplemental KW strips, and loop gets closer to 34F since 2005.

Thanks Chris !

"1000 bucks/ 300'  "  COME TO PA NOW !!!!!

Dana all $ before credits/rebates.

Curt:
Seems 77-deg entering is all I find on GEOCOMFORT  www.Enertechgeo.com  -data, as was for COOLING (absorbed overall) ratings like was since the 1980's.  Loops over 88deg. EF/EW/EL better get near 4gpm per compressor-labled ton (12MBtu's) in any GT/Chiller box, or rack, - for any "high" efficiency. Now the pressure-drops and pumping horsepower of less than 17 tons or so per 1hp pumps (calc) will put all GT-er's in D1's range of mathematical arguement(s). - Not quarrelling, just the postulates to in-situ results to answer his valid arguements.  Dana: The head/suction - pressure/temps gauge readings, per install, tell your story, as you well know
knotETUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
26 May 2012 07:45 AM
Posted By robinnc on 25 May 2012 10:14 PM
Dana......to get the price down to 6K/ton up there.....get ride of the unions     :)

sshhhh youz !  they keep me busy gettin' mo' work! Profitablility for Performance Contracting prevails/ and gets me their rate of wages and more.
chrisbikerUser is Offline
New Member
New Member
Send Private Message
Posts:97

--
29 May 2012 10:29 AM
Posted By Dana1 on 25 May 2012 04:28 PM
Chris- Clearly that would be a super-bargain, in my neighborhood! (Even your high-bid of $30K for 4-tons would beat the local average here by about five grand, but it's likely that SOME 4T system here would hit that number.)

You probably took the 30% tax credit, bringing the out-of-pocket to about $16K before other state & local subsidies? What was the final post-subsidy cost?


Dana-  We did use the 30% Fed credit and also $900 or so local utility rebate.  I payed another $800 for yard repairs. It was a mucky mess inside the hay bales.  Net cost around $16K.  We have red clay and shale here.  Driller had no issues except lots of water starting at 60 ft.  We used thermal grout and clip spacers on 1" HDPE. 

Not sure what your soil type is and if that ups costs in your area.

System in super comfortable for us.  Love the dehum low fan speed on super humid spells like now.

I added a relay off Y2 to the second loop pump, so we only use (1) 26-99 for most of the time to save on pumping power.  We leave the resistance breakers off all the time.  could have gone with 3 or 3.5 ton, but Man. J said 4T....

Higher end ASHP was in $9-10K range.  Late night winter output was considerably lower if we went with ASHP.  I was toying with upping to 5T ASHP to limit resistance, but swayed to GEO.  Ducts would be pushed a bit in that route.

Maybe some Pa guys can make some money in your area??

Chris


joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
29 May 2012 12:01 PM
"We leave the resistance breakers off all the time. could have gone with 3 or 3.5 ton, but Man. J said 4T...."

To be clear, manual J didn't say 4T, the system designer did. That you never employ auxiliary would suggest you are significantly oversized if you are in a northern climate and therefore could have purchased a smaller unit for thousands less.
That said, larger unit may be much less expensive to operate (justifying extra install expense) depending on the cost kwh of electricity in a given AO.
In an area like mine where electricity is cheap, the larger unit occasionally costs more to operate.
We also tend to look at higher set points down the road if it is somebody's forever house. If they want 68* now, we might op cost compare 75* for waning years and blood thinners- in these cases folks may choose a slightly heavier design (that depends less on electric aux. at higher set points).
All designs are compromises, inst vs op cost, heating vs cooling driven etc. Many designs are okay when informed choices are made. Simply wanted to remind that aux is not always the antichrist it is made out to be.
j
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
ChrisJUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:277

--
29 May 2012 12:29 PM
"therefore could have purchased a smaller unit for thousands less"

How much of the "thousands less" would be just the packaged unit itself?

Reason I ask is my installer sold me a 5-ton unit, then reduced it to a 4-ton but never changed the invoice, my copy still says 5-ton.

The unit still has to have all the same components, just a lttle different size.

ChrisJ RI
ChrisJUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:277

--
29 May 2012 12:29 PM
"therefore could have purchased a smaller unit for thousands less"

How much of the "thousands less" would be just the packaged unit itself?

Reason I ask is my installer sold me a 5-ton unit, then reduced it to a 4-ton but never changed the invoice, my copy still says 5-ton.

The unit still has to have all the same components, just a lttle different size.

ChrisJ RI
ChrisJUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:277

--
29 May 2012 12:31 PM
"therefore could have purchased a smaller unit for thousands less"

How much of the "thousands less" would be just the packaged unit itself?

Reason I ask is my installer sold me a 5-ton unit, then reduced it to a 4-ton but never changed the invoice, my copy still says 5-ton.

The unit still has to have all the same components, just a lttle different size.

ChrisJ RI
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
30 May 2012 10:19 AM
In my AO, horizontal ground loops are about $1650/ton and verticals 1 thousand more. Incremental price difference for the next larger heat pump maybe as much as $500.
So loosley two to three thousand.

I don't know what the conversations were with your installer, sometimes I discuss one thing and write another etc. (honest mistakes are made), but you clearly didn't need a 5 ton if you don't run auxiliary on the 4 ton. Frankly it would very likely cost more to run than the 4 ton.
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
ChrisJUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:277

--
30 May 2012 10:38 AM
Thanks Joe,

Figured it was mostly loop costs. In my case the loop was on a seperate invoice, they reduced from 6 trenches to 5, 200' ea w/ 1" pipe, my excavation guy. Returned the cost of 1 HDPE pipe. Honest mistake maybe, or $500 on almost $28,000., peanuts.

If the house was just water to air we could have done 2 tons, but with radiant and DHW 4 tons is good maybe still a little oversized.

ChrisJ
chrisbikerUser is Offline
New Member
New Member
Send Private Message
Posts:97

--
30 May 2012 11:59 AM
Posted By joe.ami on 29 May 2012 12:01 PM
"We leave the resistance breakers off all the time. could have gone with 3 or 3.5 ton, but Man. J said 4T...."

To be clear, manual J didn't say 4T, the system designer did. That you never employ auxiliary would suggest you are significantly oversized if you are in a northern climate and therefore could have purchased a smaller unit for thousands less.
All designs are compromises, inst vs op cost, heating vs cooling driven etc. Many designs are okay when informed choices are made. Simply wanted to remind that aux is not always the antichrist it is made out to be.
j
Joe,
Agreed.  My system is oversized.  I did not intend to imply that Aux heat is such a bad thing on a properly sized system.  All of the vendors figured our house would need Aux with the 4 ton.  Balance point was somewhere from 22 -28 deg F (IIRC) depending on the contractor.  I guess our house just is a little tighter than their calcs showed.  I could have saved a few bucks going to a smaller unit, but I am more than happy where we ended up. 

I do burn some wood on cold nights in our catalyst insert, but not all the time.  I have a TED monitor so I can see all stage run times.  On some single digit nights, second stage ran for 2+ hours straight (no wood burning) so I think my balance point is close to that.   KwH consumption very closely tracks HDD's unless there is tons of solar gain on the day or very windy.  Neat to plot and see.  I can tell which days we burned some wood from the plot.   I rough calced that its a tad cheaper to run the geo at 0.15/Kw, than burn wood at $200/cord.  Great system.

Chris
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
30 May 2012 12:25 PM
yikes .15kw would make you wanna keep the balance point low.
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!


---