Posted By Jeff from KY on 03 Mar 2010 03:00 PM
Quick question on wall R values. Our house is also earth sheltered. Approximately half of the walls are 10" thick poured concrete with 2" of rigid foam insulation on the outside, with all except the top 18" underground. Should I use an R value of 10 (just the foam) or should I increase the R value for the concrete and the earth sheltering? Thanks.
Since the cold-side of the foam is dirt at a relatively constant temp closer to the average annual air temp at the bottom, maybe close to the seasonal average temp at the top, it won't be anything LIKE the heat loss against your design-day outdoor air temp of (guessing here) 5-10F. from a modeling point of view it's probably closer to treat the earth sheltered wall surfaces as if they were insulated slab rather than wall. It's 40-55F dirt you're insulated against on those sides not 5F air, and it'll be a small fraction of the total heat loss.